Afternoon Gentlemen,
Been lurking in here for a while; absorbing the knowledge and passing it off as my own ideas and understanding ;) In between my extensive on-site research in to Yorkshire Teabags versus PG Tips I've written some notes (attached as a PDF) to get my head around two way switching with power to the switch. This appears to be the standard my qualified colleagues (God 1, God 2 etc) work to. Can I ask you to look over it and tell me if I'm on the right lines. I've left out the obvious, insulation tape on the screw connectors etc.
Thanks for all you help to date.
 

Attachments

although that will work, that's a rather dated way of doing it. and forget tape on choc blocks. use wagos.

the more common method is to loop in at light, take a switch wire to nearest 2 way switch, brown to L1. blue (sleeved brown) to L2. then 3 core to switch 2. usually Black to C, brown to L1, grey to L2. ( sleeve the black and grey).
 
Welcome along.
The first part is OK with the one way switching, the loop in and loop out can go in any common terminal but you want to minimise the cores you need to terminate in each terminal so splitting them up is good.
For the two way switching the writing below the diagram is referring to three wire switching that Telectrix has described above (for a loop in rather than switch fed arrangement) but the diagram is showing two wire switching and also transferring the neutral. In the case shown in the diagram the three core cable would be brown to both L1, Black sleeved brown to both L2, and grey sleeved blue to connectors for the neutral at each switch.
Try again for the two way switching.

some diagrams to either help or confuse the issue:
Slide1.JPG Slide2.JPG
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Marti

Arms
-
Joined
Location
Poole, Dorset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Jigsaw Electrical Services

Thread Information

Title
Apprentice's Question on 2 way with power to the switch
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Marti,
Last reply from
Marti,
Replies
3
Views
1,504

Advert

Back
Top