The IET seem to think they are compliant, as they are suggested as a method of providing RCD protection within installations on p36 of the OSG
If you could fit an rcbo board for just a fraction more money than a split rcd board then why on earth would anyone fit the rcd board.
an rcbo board or better in every way thinkable
very rarely, but when it happens the disruption to loosing half the houses electrics is why RCD split board is a poor choice.How often are you expecting the RCD to trip in a normal domestic?
very rarely, but when it happens the disruption to loosing half the houses electrics is why RCD split board is a poor choice.
More to do with one circuit breaker protecting one circuit disconnecting will not effect another , as the regulations allow more than one circuit to be collectively protected by one rcd.Commonly installed but the regs do state that the failure of one circuit shouldn't effect another circuit.
Similar situation with SY cable. It's not a BS7671 recognised cable but widely used.
More to do with one circuit breaker protecting one circuit disconnecting will not effect another , as the regulations allow more than one circuit to be collectively protected by one rcd.