W=I*V
Input power x ((1/Efficiency)+1) = Output power.
So 1000W O/P @95% efficiency = 1010.526W I/P.
Most of the places I’ve worked we used 433/250V some of the earlier plants used 550V or 660V. (The higher the voltage, the more power you can cram down a cable).
As an experiment I lowered the voltage at our intake sub. I got nothing but complaints from across the works and two local villages. I’d lowered it to give 400V nominal.
400/230V is, in short, impractical.
To lower the voltage to our works and the villages I turned the AVR down on the 4 20MVA 33/11KV transformer OLTC (On Load Tap Changer). Soon turned it back up again, problems were flooding in from all over.
This all came about due to a problem with cheap crappy VSD’s on one plant. We did change the local tap changer there.