In the oil and gas industry (working around hazardous areas), I commonly see conduit seals in places that they should not have been installed, but not being able to wait for the conduit to be re-done due to project startups, the seals are left as they were installed. Oftentimes, these do not get poured since they were unnecessarily installed in the first place (justs costs extra money to install them). I've had a few electrical inspectors mention that the NEC code requires these seals to be poured if they are installed, but I can't seem to find evidence within the code to backup this claim. Any help or suggestions?
 
In the oil and gas industry (working around hazardous areas), I commonly see conduit seals in places that they should not have been installed, but not being able to wait for the conduit to be re-done due to project startups, the seals are left as they were installed. Oftentimes, these do not get poured since they were unnecessarily installed in the first place (justs costs extra money to install them). I've had a few electrical inspectors mention that the NEC code requires these seals to be poured if they are installed, but I can't seem to find evidence within the code to backup this claim. Any help or suggestions?
You need to read articles 500 and 501 it states all seals be poured. It’s common sense that without the seal not being poured explosive fumes can get in the panel. If you don’t need that particular conduit just cut the pipe at the panel and install a plug in the pipe and a good tight hole seal for the panel and your problem will be solved. Maybe in the future someone will need that conduit for something else. Good luck
 
You need to read articles 500 and 501 it states all seals be poured. It’s common sense that without the seal not being poured explosive fumes can get in the panel. If you don’t need that particular conduit just cut the pipe at the panel and install a plug in the pipe and a good tight hole seal for the panel and your problem will be solved. Maybe in the future someone will need that conduit for something else. Good luck
I think you misunderstood my question and scenario. I understand that it is common sense to pour seals where they are needed and required by code, but I'm referring to specific instances of seals being installed in error (where they wouldn't be required by code) - whether those seals installed in error must be sealed or not. Also, this is referring to instances where the conduit is needed and being used so your last couple statements are not related to my scenario.
 
In the oil and gas industry (working around hazardous areas), I commonly see conduit seals in places that they should not have been installed, but not being able to wait for the conduit to be re-done due to project startups, the seals are left as they were installed. Oftentimes, these do not get poured since they were unnecessarily installed in the first place (justs costs extra money to install them). I've had a few electrical inspectors mention that the NEC code requires these seals to be poured if they are installed, but I can't seem to find evidence within the code to backup this claim. Any help or suggestions?
According to the NEC all sealoffs must be poured in a class 1 division 2 or class 1 division 1 environment. It’s up to the authorities having jurisdiction. I’ve worked in many classified areas and always poured the sealoffs. The plant engineers make that call. Look up article 501 classification of hazardous locations in the NEC
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Oklahoma City
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Are unnecessarily installed conduit seals required to be poured by code?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
redraider2010,
Last reply from
Megawatt,
Replies
3
Views
1,756

Advert

Back
Top