I have a customer who is having Pod Point install one of their chargers at a car port, some distance from the house.

SWA (10mm2) for the supply will be run to a small consumer unit at the car port, with the Pod Point installed adjacent.
A 2-core cable is also required to connect the Pod Point to an energy clamp back at the house intake.

Pod Point have specified a 7-2-2C PVC screened cable as suitable for the energy clamp - but this would need to be run e.g. in conduit.

The route is partially under the lawn, and ideally this 2-core cable would be an SWA type in the same trench.
Is there an armoured version of the above cable, or can someone recommend a suitable type?

I'm tempted to just suggest 1.5mm2 standard 2-core SWA, but I've no idea how critical the screening is.
Nor if Pod Point would throw a wobbly when they turn up if the cable is a bit bigger than they expect, with SWA they can't terminate.
 
The above cables look interesting, but don't go above 6mm2, and unfortunately the cable needs to be 10mm2 for (voltage drop).
 
BS 5308 part 1 type 2.

Screen pairs in SWA.
 
  • Like
Reactions: pc1966 and SJD
7.9mV /A /m
Must be a long run?
 

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SJD

Mentor
Arms
~
Joined
Location
Braccan heal
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
Running own small electrical company.

Thread Information

Title
Armoured Pod Point energy clamp cable?
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
SJD,
Last reply from
pc1966,
Replies
5
Views
4,819

Advert