Can you print the report, redact personally identifiable information (including the report number at the top of each page - this includes the membership no.) using a marker pen, photograph it and upload it? Or digitally copy it and redact it?
Without more information it's hard to establish whether there is any basis for the observations and even with the report it may be difficult.
The item about the RCD being incorrectly wired for example... if it's a split load board then it's very hard to wire them incorrectly. If it's a main switch, it's hard to wire them incorrectly.
With regards to the main earth being undersized... there are a number of factors at work here... if it's say 6mm and there are no signs of thermal damage I would be inclined to code it as a C3. If RCDs are present, I'd definitely code it C3 as the RCDs should prevent any sizeable earth fault current being maintained for a significant period of time.
Whilst not quite the same, I would apply the same logic to the bonding, for the same reasons.
That being said, these are just comments off the top of my head and without the full report (and the experience of seeing the installation) it's hard to provide better feedback.
As SC says, more info please.
The undersize main earth & main bonding, what size do you have? What is the earthing arrangement?
Assuming you are in Nutley (I'm very very close) then typically the bonding to gas/water was undersized when built at 6mm2, and I'd generally give a C3 for that.
As mentioned, post more details, including the sheet of test results. And perhaps a photo of the consumer unit.
While the installation might turn out to benefit from a new consumer unit, the observations should be listing the issues, not mandating the solutions.
Reply to Assessment of EICR codes in the inspection report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...