Can you print the report, redact personally identifiable information (including the report number at the top of each page - this includes the membership no.) using a marker pen, photograph it and upload it? Or digitally copy it and redact it?

Without more information it's hard to establish whether there is any basis for the observations and even with the report it may be difficult.

The item about the RCD being incorrectly wired for example... if it's a split load board then it's very hard to wire them incorrectly. If it's a main switch, it's hard to wire them incorrectly.

With regards to the main earth being undersized... there are a number of factors at work here... if it's say 6mm and there are no signs of thermal damage I would be inclined to code it as a C3. If RCDs are present, I'd definitely code it C3 as the RCDs should prevent any sizeable earth fault current being maintained for a significant period of time.

Whilst not quite the same, I would apply the same logic to the bonding, for the same reasons.

That being said, these are just comments off the top of my head and without the full report (and the experience of seeing the installation) it's hard to provide better feedback.
 
As SC says, more info please.
The undersize main earth & main bonding, what size do you have? What is the earthing arrangement?
 
Assuming you are in Nutley (I'm very very close) then typically the bonding to gas/water was undersized when built at 6mm2, and I'd generally give a C3 for that.

As mentioned, post more details, including the sheet of test results. And perhaps a photo of the consumer unit.

While the installation might turn out to benefit from a new consumer unit, the observations should be listing the issues, not mandating the solutions.
 

Reply to Assessment of EICR codes in the inspection report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
407
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
534
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
534
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock