Is this a brand new boiler and is the installation complete, apart from the hopper auger not working?

If so it seems it must be on a VSD (inverter drive) and the drive is shutting off when it detects the motor connected.

If you've had 230 on the cable to the motor, connected at the boiler end then the problem is in the boiler control.

Definitely a job for Veissmann.
 
Motor is not run through an inverter as far as I can see.
its a brand new boiler and the install is complete all working apart from auger.
could the inverter be an internal component that I can not get to?
no overload settings to alter I'm afraid.
certainly looks like a job for the veissmann tech guy whose back tomorrow morning.
 
photo

heres one
 

Attachments

  • 2013-02-28 09.37.39.jpg
    2013-02-28 09.37.39.jpg
    160.2 KB · Views: 77
Auger motor(2).jpg
Hi,
Thank you for motor label picture


So,
Second picture:
German induction motor:90w/230v,50Hz, mechanical reduction and & thermal protection.
The only protection you got can cut the power. You got probably 2, 3 wires available.

Only if you are an electrician you could follow the next steps.

a. Identify the phase and neutral properly and see the coil resistance.
(Roughly 500-600Ω should be all right). If phase- neutral it is ..MΩ the thermal protection from coil needs to be replaced.
b. Energize external the engine (230v).
c. If you keep the mechanical reduction the speed should be 1/min. - very slow.
Thank you. Good luck.

I look forward hearing from you.

Bertt.
 
Evening all thanks for all of your input.
had Veismann out this morning and after a few hours of trying this and that it transpires that it was a couple of settings on the control panel after all.
had a feeling it would be something simple in the end. Part of me was a bit disappointed after all that .
 