Morning,
I’ve only ever used a kewtech MFT and I’ve bought a Megger 1710

On the back of the tester above I have the following colour coded terminals for the test leads.
L3 Blue
L2- Green
L1+ Red

Q1. What leads should I plug in to do the end to end tests on a ring final circuit.
Doing the
L - L
N-N
CPC to CPC to get r1 r2 rn


Q2. Testing at the sockets using the supplied socket testing lead.

When I cross connect L +N do I need to connect L3 blue and L1 Red leads at the back of the tester.

When I cross connect L +CPC do I need to connect L2 green and L1 Red leads at the back of the tester.

Thanks in advance for any help - I cant make sense of the manual or maybe I haven't read it properly.
 
Last edited by a moderator:
Combining details from the instruction manual:
Connect two test leads to the L1 (+ve) and L2 (-ve) terminals on the instrument. A continuity measurement is made automatically.

For Live to Neutral measurements, connect the Red connector to the L1(+ve)terminal and the Blue connector to the L2(-ve) terminal.
For Live to Earth measurements connect the Red connector to the L1(+ve)terminal and the Green connector to the L2(-ve) terminal.
 
Last edited:
Thanks for the quick replies - I have a day off today due to clunking my head a big nail hanging out of a joist yesterday, and needed to be stitched up. :-)

I'm going the test the two ring final circuits in my own house.
I watched the the video recently but it confused me a bit because he has a black lead which I haven't got.
I'm guessing the L3 terminal only comes into play on three lead tests. ?
 
what colours are your leads?
 
so the blue will be substituted for black. if the MFT is 2nd hand, someone has swapped a duff lead.
 
Thanks for that, I bought form a budget website - brand new. Probably £30 quid cheaper than most places.
I hope it's not dodgy.
 
I might speak to megger UK for clarification. I registered it on the Megger website when I bought it.
 
I think the current colours are the same as you have the instruction manual shows red, blue and green.
 
Thanks again I have completed the tests, recorded my results I'm going to check later if it meets the regs.
I have a fair idea they do cos I didn't get any 'out of the ballpark' readings.

My CU is in a infuriatingly awkward position under the stairs with no room to maneuver.
I only had to change the leads on one of the figure of 8 tests. the L-Ns
 
My Megger test leads are Red Blue & Green. A new set.

For R1+RN test, use the Red & blue in there usual respective sockets and it will work as normal.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
basic question on MEGGER 1710 MFT.
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
newtothis,
Last reply from
newtothis,
Replies
12
Views
198

Advert