God morning, I fitted a 6 waysplit BG consumer unit the other day and the right side, starting at the main 100 amp switch have burnt out, literally flames and melted the fuses!!!....it is a 3 bed house with the usual mains/lighting/10kw shower etc and they have a PV system. After the meltdown I attended immediately and replaced all damaged equipment and re energized, no problems, I also disconnected the PV system in case that was causing a huge spike. Everything tested fine at 246v 50hz. After the system had been on for about 6 hours, again in the space of 5 mins it went from cool regular fuses to darn hot!!...of course I wasnt there to witness it so couldnt measure the current etc, but told the home owner to leave it off and attended AGAIN later, when all nice and cool and powered up fine!!!!....Any ideas would be greatly appreciated, and NO they dont have a cannabis farm!!!.....Jon Little....tel **********
 
Last edited by a moderator:
What testing did you carry out before turning the power back on again?

This was my 1st thought, it obvious that there is a serious fault on the installation and I would not advise you keep switching it back on and Buggering off.
Get back round there kill the power and get your tester out.
 
Not sure what the OP is stating here, eg..... ''After the system had been on for about 6 hours, again in the space of 5 mins it went from cool regular fuses to darn hot!!...''

Are you saying that the PV system was turned back on after 6 hours and the breakers got hot within 5 minutes, or that breakers suddenly got hot within 5 min's after being on for 6 hours??
 
Have you actually used a screw driver to tighten up the terminals? if so did you use the correct driver? if so did you look at the existing installation to see what the load would be? if so did you put a clamp meter around the mains tails and switch everything on after the first fire to see what the load actually is? if so did you re-test the installation after the first time to see if any readings are different? if so did you check your tester to see if it is working, if so have you got a yellow pages? if so go to the "E" section and ring for an electrician to come along to take a look.
 
Have you actually used a screw driver to tighten up the terminals? if so did you use the correct driver? if so did you look at the existing installation to see what the load would be? if so did you put a clamp meter around the mains tails and switch everything on after the first fire to see what the load actually is? if so did you re-test the installation after the first time to see if any readings are different? if so did you check your tester to see if it is working, if so have you got a yellow pages? if so go to the "E" section and ring for an electrician to come along to take a look.

But Mike mate he is an electrician????????
 
@OP. i see your location is close to me. if you're struggling i can attend and advise. this situation needs to be resolved before a tragedy occous.
 
Everything tested fine at 246v 50hz.
That statement disturbs me mate, what other tests were carried out when the first CU was installed? It was irresponsible to re-energise this installation, there is possibly a serious fault there although my money (like others) is on loose terminals.
 
Trev, many thanks for your reply, there are no loose terminals and I ran a full set of tests before and after energising for the first time and more since!!...:(
 
Hi dude,if none of the OCPD's on that side of the board have tripped,and it is failing the same,in the same spot,i would go for a board build error (not necessarily your error) as on that few number of ways,you should not be easily able to overload one section to that extent. I would NOT let go of this bone without finding solutions. Even if you,yourself cannot see an anomaly on the board you have fitted,you should re-fit another board,same or otherwise,as the seriousness of this issue,warrants it. PLEASE let us know your findings.:pirate:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
BD consumer unit main fuse and right side of RCD and MCB's burning out
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23
Unsolved
--

Advert

Thread statistics

Created
tlijl,
Last reply from
Marvo,
Replies
23
Views
3,112

Advert

Back
Top