- Aug 30, 2011
- 644
- 493
- 137,226
- If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
- United Kingdom
- What type of forum member are you?
- Electrical Engineer (Qualified)
in the old bpg4 it stated
Absence of supplementary bonding for installed Class II equipment where required (such as
in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future.
as:
Non-compliances with the current edition of BS 7671 that do not give rise to danger and do not require reporting.
In the new bpg4 (dec 2022) it only states:
Absence of supplementary bonding where required, in
a location containing a bath or shower, unless all of the requirements of Regulation 701.415.2 permitting omission are met is a :C2
Has the advice on class 2 only equipment in a bathroom been changed? or
would this be under “not required” as there are no simultaneously touchable exposed and extranous conductive parts
as:
- TL;DR
- coding EICR with BPG4