Discuss Boiler control circuitry in the Central Heating Systems area at ElectriciansForums.net

spud1

-
Arms
Reaction score
55
We are currently doing a site of 15No. new build houses. The 15No. plots are the last of 40No. approx on the site (We have taken over from another electrical contractor who has been thrown off site).

The previous electrical contractor has wired the supply for the S Plan boiler control circuitry in the previous 25 plots in an odd way. Whereas I would normally have a switched fused spur in the airing cupboard adjacent to the wiring centre for isolation of all control circuitry and a 3 pole isolator at the boiler position for isolation of the boiler (P Live, switch live and neutral) only, they seem to have wired the supply to the wiring centre through two switched fused spurs (in series) the first at the boiler location and the second adjacent to the wiring centre.
I see how this serves the purpose of isolation of all control circuitry (including the boiler itself) from both locations but its seems to me rather odd practice to have 2No. switched fused spurs in series like this. I think it increases the likelihood of confusion during future fault finding (e.g. one fuse blows, engineer attends to correct and finds the other fuse intact and rightly assumes this is the only fuse protecting the boiler circuitry). I also think it increases the potential of accidental energizing of the control circuitry and wiring centre while being worked on in the future (e.g. Heating engineer swaps a faulty cylinder stat in the airing cupboard in 5 years time, isolates from switched fused spur adjacent to boiler downstairs only, customer comes home and inadvertently turns the spur back on not knowing it is being worked on).

Would appreciate your opinion on this one?
 
(e.g. Heating engineer swaps a faulty cylinder stat in the airing cupboard in 5 years time, isolates from switched fused spur adjacent to boiler downstairs only, customer comes home and inadvertently turns the spur back on not knowing it is being worked on).

Would appreciate your opinion on this one?

It doesn't seem the most logical way, but most boiler set ups I've seen only have 1 fused spur to isolate the whole circuit, and that could be sited anywhere.

In a house it's unlikely someone would not know of the presence of a tradesman.
The person working on the equipment should have it suitably isolated, locked off where possible and a warning notice displayed.
 
Very true, safe isolation and locking off at the consumer unit would be the proper action during any maintenance, my example is assuming the engineer who is carrying out the work is'nt necessarily a competent electrician but maybe a heating engineer/plumber who would be less likely to be aware of safe isolation procedures. My example regarding the homeowner inadvertantly energising the control circuitry again is an assumption of perhaps another family member coming home not knowing someone is working on the boiler control. We have always installed 1No. switched fused spur to isolate and protect all control circuitry but always site 3pole isolation next to the boiler too for local service isolation of that boiler.
 
All the time I've done heating systems I've never fitted two fused spur, I've always put the spur in a logical place, combis next to the boiler, y and s plans either next to the boiler or wiring centre depends which type of boiler it is and how it wired. Surely one of the spurs should just be a double pole switch then only one fuse can blow
 

Reply to Boiler control circuitry in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi, The house I've moved in to doesn't have an extractor in the main bathroom so I'm looking at placing an inline extractor in the attic directly...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock