Discuss Bonding main water PVC in the UK Electrical Forum area at ElectriciansForums.net
Hi all,
In a bit of a quandary,main water incomer is PVC ,from stop cock in property all copper.
Now,do I bond the copper or not,read OSS and it only says recommends bonding to copper,I've been on other forums and had mixed replys,50% say yes,50% say no.
Any thoughts?
Measure from MET to copper pipework and see if it is below 22.5 kOhms, if it is, you will have to bond it. If not you are OK. Make sure there are no electrical items connected to the pipework for the test i.e. boiler.
Official line is....if the incoming service is plastic but the internal installation is all metallic, bonding is "recommended" unless the test as SS has described above, proves that the internal pipework does not meet the definition of an extraneous-conductive-part.
Is this in the regs Lenny ? Not a trick BTW a genuine one I have GN8 on order so maybe it's in there but I can't find it in the BGB
ATB J
Cheers all,so as SS says if i test from met to pipe work and the reading is above 22.5 k ohms I'm ok,
I havnt got gn8 will have to invest in a copy.
I presume it makes no difference if it's a TT system.
Cheers all,so as SS says if I test from MET to pipe work and reading is above 22.5k ohms I don't have to bond,does it make any difference that's it's a TT system?
I haven't got GN8 will have to invest in a copy.
Reply to Bonding main water PVC in the UK Electrical Forum area at ElectriciansForums.net
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Is there still a requirement to bond the main water if everything after the stop cock is plastic? Cheers
4K
Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...