Hi all,
In a bit of a quandary,main water incomer is PVC ,from stop cock in property all copper.
Now,do I bond the copper or not,read OSS and it only says recommends bonding to copper,I've been on other forums and had mixed replys,50% say yes,50% say no.
Any thoughts?
 
Measure from MET to copper pipework and see if it is below 22.5 kOhms, if it is, you will have to bond it. If not you are OK. Make sure there are no electrical items connected to the pipework for the test i.e. boiler.
 
Official line is....if the incoming service is plastic but the internal installation is all metallic, bonding is "recommended" unless the test as SS has described above, proves that the internal pipework does not meet the definition of an extraneous-conductive-part.
 
Official line is....if the incoming service is plastic but the internal installation is all metallic, bonding is "recommended" unless the test as SS has described above, proves that the internal pipework does not meet the definition of an extraneous-conductive-part.

Is this in the regs Lenny ? Not a trick BTW a genuine one I have GN8 on order so maybe it's in there but I can't find it in the BGB
ATB J
 
Cheers all,so as SS says if i test from met to pipe work and the reading is above 22.5 k ohms I'm ok,
I havnt got gn8 will have to invest in a copy.
I presume it makes no difference if it's a TT system.
 
Cheers all,so as SS says if I test from MET to pipe work and reading is above 22.5k ohms I don't have to bond,does it make any difference that's it's a TT system?
I haven't got GN8 will have to invest in a copy.
 

Reply to Bonding main water PVC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Is there still a requirement to bond the main water if everything after the stop cock is plastic? Cheers
Replies
9
Views
4K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
575
Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Replies
5
Views
1K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
968

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock