hi guys
Just a quick question as I’m being told I don’t have to Would I have to install bonding to water and gas services if I’m to install a fan in bathroom due to it being a special location
 
you'd need to check and if necessary, install or upgrade main bonding to water and gas ( and any other extraneous parts) and also RCD protection for all bathroom circuits is essential. supplementary bonding is not usually required.
 
you'd need to check and if necessary, install or upgrade main bonding to water and gas ( and any other extraneous parts) and also RCD protection for all bathroom circuits is essential. supplementary bonding is not usually required.
Thanks pal I understand the RCD requirements just my mate said you won’t need to install bonding and just make a note on the minor works but I was sure he was wrong.
 
hi guys
Just a quick question as I’m being told I don’t have to Would I have to install bonding to water and gas services if I’m to install a fan in bathroom due to it being a special location
 
main bonding is essential when doing any work in a property.
 
Thanks guys answered my question and what I thought
 
What you mate said is different!
You the one who will issue the certificate not your mate

If I was you tell the customer tell them regs say
New bord Gas/water bonding

Small note (get the meter out and spend few minutes insulation resistance then jobs all yours
 
What you mate said is different!
You the one who will issue the certificate not your mate

If I was you tell the customer tell them regs say
New bord Gas/water bonding

Small note (get the meter out and spend few minutes insulation resistance then jobs all yours
Cheers pal
 
I see another of Buzz's relations is on here.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Bonding required when alterations in special location
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Sb8389,
Last reply from
westward10,
Replies
8
Views
1,576

Advert