What? This is just a fault that with the correct test equipment should be relatively simple to find.


[/COLOR]
What if the EICR doesn't pick up the fault?

I WOULD CHECK THE MCB AT 1ST INSTANCE might save alot of fault finding
 
What? This is just a fault that with the correct test equipment should be relatively simple to find.


[/COLOR]
What if the EICR doesn't pick up the fault?

If your test results for the fixed installation are within spec, then there is no possible reason that a healthy RCd will trip.
Unless there is an obvious wiring fault in the CU.
 
Siemens RCCB breaker, Also says next to the switch 80amps and has written 5SM13 317-0. The lights still work when it trips. Will post a picture tomorrow.

I live in a 2 bed new build flat (4 years old). We don't use excessive amounts of electricity.


In a four year old flat ?
 
Or a faulty appliance being plugged in, a time clock or thermostat turning a faulty appliance on. The list is endless a fault won't always be present on a circuit which is why a EICR may achieve nothing. But the RCCB keeps tripping even though a report says there is nothing wrong with the installation.
 
Or a faulty appliance being plugged in, a time clock or thermostat turning a faulty appliance on. The list is endless a fault won't always be present on a circuit which is why a EICR may achieve nothing. But the RCCB keeps tripping even though a report says there is nothing wrong with the installation.

but however you label it, as Rich.250 said the circuit affected need identifying and testing, along with the RCCB. If the standard tests show a problem then great, if not then you need to look further.
Now all the OP needs is a spark who knows what he is doing ;)

btw. a question for the OP - does it trip more when (or after) a lot of rain and do you have any outside sockets or lights? Or perhaps a bath or sink that has leaked recently?
 
I live in a 2 bed new build flat (4 years old). We don't use excessive amounts of electricity.


In a four year old flat ?


Its probably a split load CCU installed under the 16th ed. when the electrical design for the flats were put forward.

There are about four or five possibilities it could be.

Try this one for starters.

Switch off the dish washer/ washing machine at the local switched fused control unit. This will determine whether or not you need an electrician or an appliance technician.
 
but however you label it, as Rich.250 said the circuit affected need identifying and testing, along with the RCCB. If the standard tests show a problem then great, if not then you need to look further.
Now all the OP needs is a spark who knows what he is doing ;)

Not disputing that, it was in reference to the idea of getting a EICR carried out to find the fault.
 