Can I have some thoughts on a broken TT Earth. The house owner has cut through there TT Earth cable 3 feet up from the stake.

Can this be jointed and if so what would be a suitable connection, in an ideal world a new continuse cable would be preffered or is this the only option. I could not see anything in the regs to say this cable must be continuse or was I having a Man look as my wife refers to it.

Many thanks

Daniel
 
Acceptable methods of jointing it would be to crimp or solder
As you say a new lenghth of cable would be the best option but as long as the joint is free from becoming corroded I see no reason why not
Covering the joint in heat shrink sleeving should be adequate,allthough I believe a sheathed earth cable should be green/yellow throughout its length
The joint could also be enclosed in suitable plastic conduit if possible
 
Thank you Des for your helpa good heat crimp and clip the cable out the way of the hedgecutter then.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Broken TT earth cable
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Dismal,
Last reply from
mechelec,
Replies
3
Views
2,369

Advert