As I say, the measured 22v was between the ends of 2 of the disconnected 2 way switch wires and earth (ceiling rose earth, which was giving 230v to phase, 0v to neutral as one would expect) - in other words measured at the ends of (in theory) a piece of wire!!
altho as I also alluded to, there must be some sort of connection between the 2 ends as the landing end is rubber sheath and the hall end pvc, so altho not impossible, there should be no need for earths or neutrals around the sw wires at all?
Theres no earth wires at all in the switch boxes.
I did strongly recommend a rewire due to the age of the lighting wiring which the customer agreed was probably a good idea.. I left it with her..
 
22v will almost certainly be induced voltage - have seen it as high as 50v and able to trigger an energy saver! Caused by the run of the strappers in close proximity to themselves and others. Fit a snubber to get rid of it.

As for what is making the lamp blow - either a really naff connection somewhere that's causing arcing (probably on the neutral) or cheap lamp to start with! Lamps will operate happily in excess of 245v if all the other boxes are ticked.
 
22v will almost certainly be induced voltage - have seen it as high as 50v and able to trigger an energy saver! Caused by the run of the strappers in close proximity to themselves and others. Fit a snubber to get rid of it.

As for what is making the lamp blow - either a really naff connection somewhere that's causing arcing (probably on the neutral) or cheap lamp to start with! Lamps will operate happily in excess of 245v if all the other boxes are ticked.

50v! that is surprising - had no idea this could be so high..
I've come across the term "snubber" before but could you elucidate please? (showing my youthful ignorance now..)
many thanks for your useful input.
 
With the age of the cable id be confirming IR values before doing anything.. Id then check for external earth before doing ZS. ZS could be a fault internally on the earth which if it it not connected externally wont show.

What was IR?

22V on two way sounds like induced induction by the way..

Cough Cough..#2 :D
 
Have had same/similar event today. While doing pre-install tests on a lighting circuit picked up 50v between cpc and switched live...at two-way switching. Bungalow with almost pointless two-way switching. 2gang 2way at each end of short corridor/passageway operating luminaires about 3 to 4 metres apart. Hoping snubbers wii sort this out.
 