Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:

Not visibly damaged or defective so as to impair safety.

This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.

Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection

Also see 651.2 regarding periodic inspection and testing note (ii) in particular

I was going to look for a specific Reg tomorrow but I had absolutely no doubt that a Reg would be there to cover this.

How can anyone even think it is ok to no code this is beyond me.
 
I was going to look for a specific Reg tomorrow but I had absolutely no doubt that a Reg would be there to cover this.

How can anyone even think it is ok to no code this is beyond me.
It’s almost the same(tongue in cheek) as a burnt out pin on a socket but ignoring it on the grounds that it’s not fixed wiring.
 
  • Agree
Reactions: 1 person
Maybe lights should come under pat testing if we don’t inspect and code on an EICR
 
Is the OP coming back to make his mind up?
 
code it as FUBAR.
 
  • Agree
Reactions: Pete999
Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:

Not visibly damaged or defective so as to impair safety.

This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.

Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection

Also see 651.2 regarding periodic inspection and testing note (ii) in particular
It is worded differently in both book.
 
We never quote Reg Nos as they mean nothing to a large percentage of people. Anyone who decides not to include an item of potentially dangerous equipment in the Report should not be carrying out EICRs as they themselves are potentially dangerous.
 
  • Like
Reactions: Ian1981
The report is carried out to ensure the installation complies with BS7671 though, do you also note other defects on site such as items not being in date on PAT?
 
  • Like
Reactions: Pete999
That is a ridiculous scenario.
 
That is a ridiculous scenario.
Why is it? Where do you draw the line at what put on your report? As after all a out of date PAT could lead to a similar consequence? Wjat about light fittings that come pre wired, do we also have to strip them down too to ensure everything imternally is fine?
 
Do you not check for cpc at metalic fittings in little old dorris's lounge? Or is that outside of the electrical installation?

If you come accross an extract fan with a toasy pcb and melted internals in a bathroom do you ignore it?

Luminaires are CLEARLY equipment and form part of the installation as defined in the regs and should be inspected.

And whilst the aim of this forum is to factually assist and help each other, we can also voice our opinions, as i have done, and i stand by.
 
Do you not check for cpc at metalic fittings in little old dorris's lounge? Or is that outside of the electrical installation?

If you come accross an extract fan with a toasy pcb and melted internals in a bathroom do you ignore it?

Are we talking in the scenario of carrying out a EICR?
 
All eicrs, dont get why you had to pm me, you voiced a rediculous statement that they do not form part of the installation and i called you a "fill in the blank" because of it, if i made an equally rediculous statement i would expect to be called out for it aswell.
 
Are we talking in the scenario of carrying out a EICR?

Yes EICR see the original posts. Regs have been quoted to cover the situation. And even your own photo has shown equipment (like a light fitting) make up part of the installation.
621.2 iii

Installation deteriorated to impair safety

If I was a paying customer I would expect something to be flagged up for that. Code or not.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Burnt out ballast EICR Coding
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
39

Advert

Thread statistics

Created
Icarus,
Last reply from
Andy5678,
Replies
39
Views
5,646

Advert