Icarus
Scenario: Visibly burnt out, entirely blackened, ballast in a fluorescent fitting. Would this be noteworthy during an EICR and if so, how would it be coded? My thinking is that its an obvious fire risk.
Still an apprentice with millions to learn, any input would be appreciated.
Does the fitting comply with
416.2
Section 421
621.2(ii)
512.2
559.5.1
526.1
The internal section of the fitting is not part of the fixed wiring so unless any of the above are not complied with then its no code from me.
the fitting itself is outside your remit of testing to BS7671. as pp says. disconnect and no code. just tell customer if he wants to see where he's going , to replace fitting.
Read the definition below it?? An electrical installation is an assembly of electrical equipment. The lights clearly form part of the installation.
And which Reg number backs up the code? The regs only apply to the final connections carried out on site, cable entry in to the enclosure and the suitability of the enclosure.
Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:
Not visibly damaged or defective so as to impair safety.
This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.
Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection
Also see 651.2 regarding periodic inspection and testing note (ii) in particular
I was going to look for a specific Reg tomorrow but I had absolutely no doubt that a Reg would be there to cover this.
How can anyone even think it is ok to no code this is beyond me.
It’s almost the same(tongue in cheek) as a burnt out pin on a socket but ignoring it on the grounds that it’s not fixed wiring.
It is worded differently in both book.
We never quote Reg Nos as they mean nothing to a large percentage of people. Anyone who decides not to include an item of potentially dangerous equipment in the Report should not be carrying out EICRs as they themselves are potentially dangerous.
The report is carried out to ensure the installation complies with BS7671 though, do you also note other defects on site such as items not being in date on PAT?
That is a ridiculous scenario.
Why is it? Where do you draw the line at what put on your report? As after all a out of date PAT could lead to a similar consequence? Wjat about light fittings that come pre wired, do we also have to strip them down too to ensure everything imternally is fine?
Do you not check for cpc at metalic fittings in little old dorris's lounge? Or is that outside of the electrical installation?
If you come accross an extract fan with a toasy pcb and melted internals in a bathroom do you ignore it?
Luminaires are CLEARLY equipment and form part of the installation as defined in the regs and should be inspected.
And whilst the aim of this forum is to factually assist and help each other, we can also voice our opinions, as i have done, and i stand by.
Are we talking in the scenario of carrying out a EICR?
All eicrs, dont get why you had to pm me, you voiced a rediculous statement that they do not form part of the installation and i called you a "fill in the blank" because of it, if i made an equally rediculous statement i would expect to be called out for it aswell.
Yes EICR see the original posts. Regs have been quoted to cover the situation. And even your own photo has shown equipment (like a light fitting) make up part of the installation.
621.2 iii
Installation deteriorated to impair safety
If I was a paying customer I would expect something to be flagged up for that. Code or not.
Reply to Burnt out ballast EICR Coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Hello All So the scenario is; turn up to an EICR in a house, everything is good apart from seeing the smoke alarm on the ceiling with the head...
Hoping someone can give some input on what could be possible causes of what happened here. I am going to investigate the situation next week but...
Hi all, I've been having some issues trying to fix a fluorescent light in the bathroom. Here's the steps I've taken so far after it suddenly...
Hi, I'm troubleshooting a 'smart switch' issue which is connected to an existing fluorescent 4' 2-bulb (T8) fixture where I have replaced the...