Burnt out ballast EICR Coding

Discuss Burnt out ballast EICR Coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Icarus

-
Reaction score
0
Scenario: Visibly burnt out, entirely blackened, ballast in a fluorescent fitting. Would this be noteworthy during an EICR and if so, how would it be coded? My thinking is that its an obvious fire risk.

Still an apprentice with millions to learn, any input would be appreciated.
 
Does the fitting comply with
416.2
Section 421
621.2(ii)
512.2
559.5.1
526.1

The internal section of the fitting is not part of the fixed wiring so unless any of the above are not complied with then its no code from me.
 
the fitting itself is outside your remit of testing to BS7671. as pp says. disconnect and no code. just tell customer if he wants to see where he's going , to replace fitting.
 
Read the definition below it?? An electrical installation is an assembly of electrical equipment. The lights clearly form part of the installation.
And which Reg number backs up the code? The regs only apply to the final connections carried out on site, cable entry in to the enclosure and the suitability of the enclosure.
 
Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:

Not visibly damaged or defective so as to impair safety.

This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.

Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection

Also see 651.2 regarding periodic inspection and testing note (ii) in particular
 
Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:

Not visibly damaged or defective so as to impair safety.

This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.

Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection

Also see 651.2 regarding periodic inspection and testing note (ii) in particular

I was going to look for a specific Reg tomorrow but I had absolutely no doubt that a Reg would be there to cover this.

How can anyone even think it is ok to no code this is beyond me.
 
I was going to look for a specific Reg tomorrow but I had absolutely no doubt that a Reg would be there to cover this.

How can anyone even think it is ok to no code this is beyond me.
It’s almost the same(tongue in cheek) as a burnt out pin on a socket but ignoring it on the grounds that it’s not fixed wiring.
 
Regulation 642.2 (iii)
The inspection shall be made to verify that the installed Electrical equipment is:

Not visibly damaged or defective so as to impair safety.

This is from the 18th edition so naturally it’s predecessor may be different but I do not have the 17th available at the moment to compare.

Now admittedly this forms part of the initial verification process but I’d be prepared to use the same regulation method for periodic inspection

Also see 651.2 regarding periodic inspection and testing note (ii) in particular
It is worded differently in both book.
 

Reply to Burnt out ballast EICR Coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock