thanls for the suggestion, well, if I cant find something that will accept my current set up then I will simply have to either re-wire or loose one detector to make it 8 zonesNormal conventional is out for reasons above.
Normal addressable is out as you haven't got a loop and manufactures have quite strict rules about spurs that I'm fairly sure you couldn't meet in this case.
So that leave's the special cases....
Twinflex Pro is out as it also has end-of-line.
The only panel I can think of that MAY work is the Infinity ID2 range. I say that because it doesn't use EOL devices, it learns the devices and polls them. I believe it would still work with two radials in one zone. Before taking my word for this please check this is supported by the manufacture. After all this is a critical life saving system.
I'd still highly recommend finding a solution that kept it 'normal' and compatible with the majority of panels.
Is there no way to run a cable between any two devices and discard one of the radials to the panel so you are down to 8 zones?
Did you see my later thought - ESP Magfire 12 zonethanls for the suggestion, well, if I cant find something that will accept my current set up then I will simply have to either re-wire or loose one detector to make it 8 zones
Hi Tim, I must have missed that one... thanks, that should sort me out I guess....Did you see my later thought - ESP Magfire 12 zone
Out of interest, how did this cable monkey do the sounder circuits?Hi Tim, I must have missed that one... thanks, that should sort me out I guess....
the exact same way as all the detectors and call points... a 2 core cable (at least he used the shielded and fireproof one) from point to point...Out of interest, how did this cable monkey do the sounder circuits?
If you are saying you have 2 sounder circuit cables back at the panel it's ok. If you are saying that you have 8 sounder cables back at the panel then this all falls flat as they have EOL devices too.so he did one cable for zone 1 sounder (point to point) and another for zone 2 (point to point)
I haven't even checked if this (for the sounders) is ok... I just immediately got upset about the circuit cabling
thanks Tim, yes, I have 2 sounder cables back to the central point (where the panel will sit)If you are saying you have 2 sounder circuit cables back at the panel it's ok. If you are saying that you have 8 sounder cables back at the panel then this all falls flat as they have EOL devices too.
If the latter the only solution I can see is use a bi-wire system (e.g. Fike Twin flex pro) and combined detector/sounders, and fine a way to either lose a detector or find the simplest cable run between two devices (loft space?) as I'm not aware of an >8 zone bi-wire system.
yeah I understand it is not ideal having that many zones, I'm just trying to see what would be the best option. re-wire would at the moment be the last thing I would like to doPersonally just rewire it so it’s done correctly, you’re asking for problems in my opinion. It’s not ideal to have so many zones in such a small system. Have you considered how it and if it meets fire regs etc? Is the commissioning engineer happy for it to be possibly done the way you’re looking at now?
Hi again Tim,Another (better) possibility, look at ESP Magfire - I think they make a 12 zone conventional panel. Very basic but it might be your only option.
It would work.Hi again Tim,
what about this panel (also from CTEK)
aha... indeed well spotted Tim, I did not catch that... well, I will try to get in touch with someone to hear about this non compliant issue... and to hear if there is perhaps a panel that would support 12 individual zones and be compliantIt would work.
The thing it is does say "this panel in not compliant with EN54-2/4 and should NOT be used in new UK or European installations"....
You could do with some advice from a current fire alarm engineer as I got out of this game a long while ago, and can't give you any info about whether the lack of compliance of EN54 on that panel is an issue or not.