I have recently had an EICR on my tenanted 1st floor purpose-built flat, built in 1995. I have received C2 codes for lack of RCD as follows:
5.14 No RCD for additional protection
6.18(a) No RCD for socket-outlets
6.18(b) No RCD for supplies for mobile equipment for use outdoors (this is a 1st floor flat, when would you plug anything in for use outdoors?)
6.18(c) No RCD for cables concealed in walls at less than 50mm deep (electrician has commented that he can't check so has assumed worse case scenario)
6.18(d) No RCD for cables concealed in walls containing metal parts (again the same comment about worse case scenario)
6.18(e) No RCD for circuits supplying luminaries.

Does this really make the installation potentially dangerous, or are these suggested improvement (C3)?
 
"I think the one for use outside is justified as a C2 as many would run an extension lead upstairs to hoover their car I would put the rest as a C3.
Is there supplementary bonding in the bathroom?
 
In very general terms if there is supplementary bonding in the bathroom (should say on report) and no sockets for use outdoors then according to "best practise guide 4" (free online, google it) missing RCD on the items listed will attract C3's not C2's. It might be worth gently discussing BPG4 with your electrician.

That said, it's worth remembering that circuit breakers and older fuses are designed to protect wiring from catching fire, not protect people from electrocution. Having RCD protection is a good idea especially if renting out something.

If you post a picture of the consumer unit there might be a fairly simple way to remedy these things. I'd imagine it won't have many circuits if it's a flat.
 
In very general terms if there is supplementary bonding in the bathroom (should say on report) and no sockets for use outdoors then according to "best practise guide 4" (free online, google it) missing RCD on the items listed will attract C3's not C2's. It might be worth gently discussing BPG4 with your electrician.

That said, it's worth remembering that circuit breakers and older fuses are designed to protect wiring from catching fire, not protect people from electrocution. Having RCD protection is a good idea especially if renting out something.

If you post a picture of the consumer unit there might be a fairly simple way to remedy these things. I'd imagine it won't have many circuits if it's a flat.
1619716075379.png
 
That's a bit more complex than I was anticipating if I'm honest, and I can't quickly identify the brand from the photo? Are they fuse carriers on the right too?
 
That's a bit more complex than I was anticipating if I'm honest, and I can't quickly identify the brand from the photo? Are they fuse carriers on the right too?
Looks like MEM. If following napit codebreakers, then C2 is perfectly justified for everything that has been written there. It all comes down to who is doing the EICR but the C2s stated are perfectly justified as C2. Maybe I wouldn't have given them a C2, but the tester is well within his rights to do so.
 
Looks like MEM. If following napit codebreakers, then C2 is perfectly justified for everything that has been written there. It all comes down to who is doing the EICR but the C2s stated are perfectly justified as C2. Maybe I wouldn't have given them a C2, but the tester is well within his rights to do so.
Agree totally - I actually reworded what I typed before I posted to be less absolute about it, and my original opening asked about which scheme the tester was in, then thought I wouldn't go there.
It is MEM
I would suggest that if you had a RCD socket nearest to the exit that would meet the requirements for outside use, I would then find it hard to give any C2.
The thing is unless it is tested again he has a report that has given them C2's that requires remedial work.

My thought was that as he has two supplies and two main switches I'd wondered about swapping the RH main switch with the correct manufacturers 100A 30ma RCD, thus giving all the circuits mentioned RCD protection. I know we'd ideally try and avoid everything on one RCD these days but there are plenty of TT installations out there that cope fine. In this situation it might be the quickest and most cost effective way of addressing the issues?
 
Agree totally - I actually reworded what I typed before I posted to be less absolute about it, and my original opening asked about which scheme the tester was in, then thought I wouldn't go there.

The thing is unless it is tested again he has a report that has given them C2's that requires remedial work.

My thought was that as he has two supplies and two main switches I'd wondered about swapping the RH main switch with the correct manufacturers 100A 30ma RCD, thus giving all the circuits mentioned RCD protection. I know we'd ideally try and avoid everything on one RCD these days but there are plenty of TT installations out there that cope fine. In this situation it might be the quickest and most cost effective way of addressing the issues?
Apologies I didn't mean the whole reply to you, only the MEM part was directed to you. The rest I had meant for the OP.
 
I have recently had an EICR on my tenanted 1st floor purpose-built flat, built in 1995. I have received C2 codes for lack of RCD as follows:
5.14 No RCD for additional protection .
6.18(a) No RCD for socket-outlets.C3
6.18(b) No RCD for supplies for mobile equipment for use outdoors (this is a 1st floor flat, when would you plug anything in for use outdoors?) C2 OR C3
6.18(c) No RCD for cables concealed in walls at less than 50mm deep (electrician has commented that he can't check so has assumed worse case scenario) C3
6.18(d) No RCD for cables concealed in walls containing metal parts (again the same comment about worse case scenario). C3 BUT ONLY IF YOU HAVE METAL STUDDING IN THE WALLS
6.18(e) No RCD for circuits supplying luminaries. C3

Does this really make the installation potentially dangerous, or are these suggested improvement (C3)?
 
These things are tricky. And most on here reading it would agree with the codings that @telectrix put up.
But what are the pragmatic options for the OP?
1 - ask tester to reconsider, politely point out BPG4 disagrees (though as pointed out NAPIT Codebreakers agrees with some of them). No obligation for tester to change anything and in reality no promising escalation path. Nothing to lose though.
2 - Get it re-tested, and take pot-luck again. Most people I know wouldn't code it that way. But this could cost £200+
3 - Roll over, and RCD protection the cheapest way - get another sparks to fit a £30 Eaton/MEM 30ma RCD main switch from Screwfix. bish-bash-bosh job done.
4 - Change the board - £400+
 
These things are tricky. And most on here reading it would agree with the codings that @telectrix put up.
But what are the pragmatic options for the OP?
1 - ask tester to reconsider, politely point out BPG4 disagrees (though as pointed out NAPIT Codebreakers agrees with some of them). No obligation for tester to change anything and in reality no promising escalation path. Nothing to lose though.
2 - Get it re-tested, and take pot-luck again. Most people I know wouldn't code it that way. But this could cost £200+
3 - Roll over, and RCD protection the cheapest way - get another sparks to fit a £30 Eaton/MEM 30ma RCD main switch from Screwfix. bish-bash-bosh job done.
4 - Change the board - £400+
I have no problem with RCD protection. My issue is the need to correct C2s within 28 days and the high quote to change the whole board "urgently".
I'll take your advice about fitting an RCD main switch.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Aylesbury, Buckinghamshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
C2 code for no RCDs?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
16

Thread Tags

Tags Tags
code rcds

Advert

Thread statistics

Created
DavidL,
Last reply from
Dartlec,
Replies
16
Views
3,217

Advert

Back
Top