Hi All,

Just after some advice, I have been to a customer today and they are having there house renovated. There meter is getting moved to a external box due to floor plans changing, I am planning on running a 3 core 25mm SWA cable to the new consumer unit which is roughly 6 meters from the meter. My question is would I have to chase the cable into the kitchen floor or could I cleat it low level as the kitchen units will be fitted above the cable all the way to the consumer unit. Any opinions would be appreciated.

Jim
 
I would cleat direct as once buried you would struggle with safe zones. Done forget to fuse the cable down
 
Nothing wrong with cleating it. But explain to the Customer what you are doing and inform them that should they ever change the layout of the kitchen this needs to be taken into account.

Burying the cable wouldn't be a problem neither as long as you connect the SWA to the MET as you then wouldn't need to install it on a RCD/ RCBO.
 
What are you expecting the max demand to be? If you have a 100amp bomb I would install and 80a isolator to provide some discrimination between the fuses. And go for 16mm 3 core.
 
.....once buried you would struggle with safe zones.

didnt realise the safe zones extended to the floor ???

;-)

Indeed they do not, which is why i suggest cleat direct. Even though the swa is suitable to buried outside of safe zones, in my opinion it is still dodgy when presented with a Paslode. In this instance where the option exists to go direct it makes most sense to me
 
Indeed they do not, which is why i suggest cleat direct. Even though the swa is suitable to buried outside of safe zones, in my opinion it is still dodgy when presented with a Paslode. In this instance where the option exists to go direct it makes most sense to me

I see what you're saying but safe zones don't come into it at all in this case - it would be in the floor!
 
Cleating to the wall is fine. Just be aware that most "built-in" appliances go hard up against the wall with a recess at the base for power/water. If there's a ruddy great cable in the way, the appliances will stick out proud of the units.
 
Could you not run 25mm tails and 16mm earth in YT4 trunking Just thought it may be easier than making off a 3 core 25 mm SWA into the CU will the earth bar take a 25mm cable ?
 
Indeed they do not, which is why i suggest cleat direct. Even though the swa is suitable to buried outside of safe zones, in my opinion it is still dodgy when presented with a Paslode. In this instance where the option exists to go direct it makes most sense to me

I see what you're saying but safe zones don't come into it at all in this case - it would be in the floor!


Haha i clearly didnt register that information, ,aking my point moot. My apologies
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable run to new consumer unit
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
9706 james,
Last reply from
Farmelectrics,
Replies
10
Views
1,729

Advert

Back
Top