So call out to kitchen desperate to get hob working. Described big bang, MCB triggered to off. Turned back on and nothing. As you can't turn on the separate coils unless the unit is powered up how can you test it? Anyway did IR between L-N and got 0.23 Mohm so assumed something had gone into meltdown, replaced with new induction hob, Beko 7.2kw.
Just got me to thinking with electronic switching and no way of switching on the individual rings I wonder how you can realistically test it without taking the thing apart (if it is even worth the trouble) and testing at the physical induction coils. Anyone know of this sort of thing? I must say the cable entry to the hob was flattened/distorted and looked a likely point of shorting as it was compressed on the crosspiece of the carcase so I cut a hole at the point of the entry to allow obviation of compression. Also underneath the hob was an oven 3kw all on the same circuit with no ventilation which I don't imagine would help. This was on a 32a MCB and 6mm² supply cable. I have done the maths before someone tells me "I would never wire 10kw on to 6mm²" or something equally inane. I could only advise the customer the circuit was not adequate for the load and they should consider another point for the oven.
 
Applying diversity for a 10kw cooking load will be absolutely fine on a 32A MCB. Been doing it for years and never had a problem yet.
 
Applying diversity for a 10kw cooking load will be absolutely fine on a 32A MCB. Been doing it for years and never had a problem yet.
You aren’t allowed to use diversity on a commercial cooker/hob in a commercial setting or so I was always taught anyway as if the place is busy it’s not unheard of for everything to be running at the same time
 
In the real world for the moment we have all seen "overloaded" circuits that just go on for years no problem. Pragmatically regs aside we also know that there is no way all rings and the oven are going to be going full pelt 24/7 or yeh there would be a problem. I advised the client purely from the allowed diversity factors that you can apply and yes it is 100% for the first appliance and 80% for the second off the top of my head. So by regs you would be overloading the circuit technically. Add the fact the oven is right underneath it is not well thought out. I drilled a few vent holes to the side of the carcase where it meets the wall with a six inch gap to help matters. But that all aside remember, testing an induction hob...oh and yeh it is a very busy cafe with a small kitchen and the hob and oven are full tilt during business hours hence advising the client to use separate circuit. I would not have wired that up like that personally.
 
You aren’t allowed to use diversity on a commercial cooker/hob in a commercial setting or so I was always taught anyway as if the place is busy it’s not unheard of for everything to be running at the same time

Teach me to not read thoroughly. I had missed it's a commercial kitchen. In which case there'd be a whole host of factors to take into account as to whether it's likely to be sufficient or not. However I wouldn't install it like that in a commercial setting.
 
There's a theme here - @Vortigern has been called in to fix a few eating establishments now - did he install them or is he their Best Customer?

I would've wasted an hour taking the back off, checking the flex, ogling the innards and then told them to buy a new one :) .
 
I did want to pull it to pieces as I say just to test and find out what went wrong. But with <1 Mohm L-N thought yeh the cable has gone. So put new one in straight away. As to eating places and doing work yeh you are right quite a lot as it goes just a small part of the mosaic of an electricians life. Attended water heater failed in kitchen last week. Ariston, took the cover off pushed the teeny weeny reset button hey presto all good. Took 60 secs everyone said lo he is a miracle worker and has profit powers (bankwise!) Had a loverly curry for free they were so pleased. They just won a food award in Bristol totally organic and I was so hungry it was perfect!
 