Been bugging me.
I think there is a way to calculate how fast a particularly rated RCD should trip (rather than measuring) but I can't remember how to do it ?
e. g. If I was designing an SWA submain fed from a TT earthed installation and I needed to install say a 300mA TD RCD to acheive a disconnection time of 1sec for fault protection, is there a way to calculate at the design stage whether that RCD will trip within 1sec ( if I know the rated time delay) ?
 
I will stick me neck out,and say no.
You are not only dealing with differing types of electrical initiation,but there are also mechanical factors,such as thermal,friction and spring parts of its action.

The measured values have a time,but the expected,are always more than/less than.

.....But you calculate your aim point,for a 50 cal,with gravity,wind,earth spin and many other factors,so.....
 
I would suggest looking up the data sheet for the RCD in question. You'll see the I/t curves have fairly steep sides which include manufacturing tolerances and the best you can calculate is to ensure your design falls on the "will trip" side.
 
As far as I am aware the actual time in which an RCD will trip is determined by the manufacturer of the device.
Different makes of RCD/RCBO will trip at different speeds and even then the same manufacturer might have different variabilities in the speed of tripping.
However for all modern unadjustable RCDs if the fault current is 5 * rated current or more they must, to be compliant, trip within 40ms if not time delayed at least 150ms if time delayed.
In preparing a design you should be able to rely on these values to determine if the installation is safe.
 
Quick enough to save a human (if they need saving !)
, and it's self from
thermal damage.
So this will vary by :-
a) Manufacturer-
b) Bulk of material
c) Quality of materials used
d) May correlate with price/safety margin/cycles good for
 
Last edited:
Hi all.

Been bugging me.
I think there is a way to calculate how fast a particularly rated RCD should trip (rather than measuring) but I can't remember how to do it ?
e. g. If I was designing an SWA submain fed from a TT earthed installation and I needed to install say a 300mA TD RCD to acheive a disconnection time of 1sec for fault protection, is there a way to calculate at the design stage whether that RCD will trip within 1sec ( if I know the rated time delay) ?
Adiabatic equation
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Can I calculate how fast an RCD should trip?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
Deleted member 26818,
Replies
9
Views
6,010

Advert

Back
Top