We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is earthing connected to the main gas pipe 1 meter after it enters the property. Can we go ahead and remove all the redundant gas pipes including the earthing or do we need to take the earthing into account somehow?
 
We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is earthing connected to the main gas pipe 1 meter after it enters the property. Can we go ahead and remove all the redundant gas pipes including the earthing or do we need to take the earthing into account somehow?

Does the earthing (bonding) loop on to anywhere else?
 
Does the earthing (bonding) loop on to anywhere else?
Yes however not in a way that looks particularly safe!
20230205_130106.jpg
 
From your photo, you wont know which one of those green/yellow wires is the gas bond...
One from the main supply cable, one going to water maybe? What are the others?
Leave it connected, as disconnecting the wrong one could cause an issue later on.

If the gas pipe no longer enters the building, and you're removing the pipes within the property.... the bonding cable isn't doing anything..... there's no harm leaving it coiled up somewhere under the floor....
Likewise, there's no harm in removing it systematically from the gas meter position back to the consumer unit as you uncover its route by lifting boards etc.

However, as @DPG mentions in #2, make sure the gas bond doesn't then loop from the gas pipe onto the water pipe or other service... or you'll be disconnecting both.
 
From your photo, you wont know which one of those green/yellow wires is the gas bond...
One from the main supply cable, one going to water maybe? What are the others?
Leave it connected, as disconnecting the wrong one could cause an issue later on.

If the gas pipe no longer enters the building, and you're removing the pipes within the property.... the bonding cable isn't doing anything..... there's no harm leaving it coiled up somewhere under the floor....
Likewise, there's no harm in removing it systematically from the gas meter position back to the consumer unit as you uncover its route by lifting boards etc.

However, as @DPG mentions in #2, make sure the gas bond doesn't then loop from the gas pipe onto the water pipe or other service... or you'll be disconnecting both.
I don't think it loops with anything else. The end of the earthing cable goes back to the fuse.
Outside they installed this where they removed the meter.
IMG-20230429-WA0005.jpg

IMG-20230429-WA0006.jpg
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Can I remove gas earthing?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
Ericsson,
Last reply from
Ericsson,
Replies
6
Views
2,515

Advert

Back
Top