Hi - first-time post from a complete novice.
I want to install a 24kw electric boiler on my property but that size requires Phase 3 supply. Northern Powergrid don't install Phase 3 in my area (off grid) but can increase capacity via a split supply. Can I run a phase 3 boiler from a split supply?
I assume not as it is likely to depend on the specification of heaters in the boiler - but I'm just guessing.
TIA
Short answer is NO.
you may be better with 2 single phase boilers, that could be done.
Depends how the heaters are configured. if they are, or can be, star connected, then you can run two of the elements in series across the 430V supply, but the total load would be 16kW, not 24kW.
Reply to Can I run a Phase 3 boiler from a split phase supply in the DIY Electrical Advice area at ElectriciansForums.net
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
I have an old Migatronic Automig X 200 welder configured as 380V 3-phase unit. Migatronic for spec. I have a 220V 3-phase point in my garage...
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...