Can you feed a consumer unit from another consumer unit, It would be supplied by a non RDC protected MCB. Is this allowed as I have always seen switched fuse disconnection units.
 
Depending on the circuit design, then yes…. It’s allowed.

More details please for more explanation.
CU sizes, cable type and size, breaker size, environment….



Welcome to the forum
 
I often do it this way for small extensions / kitchen refurbs etc especially when the exisitng board has a nice spare way.
 
Just to add to the above, it is a perfectly good way of feeding a few circuits elsewhere, such as garage, etc.

However, you get poor fault selectivity on MCB feeding MCB. Basically if your final circuit has a PFC that is able to hit the upstream MCB's "instant" magnetic trip point then both MCBs will fire, and so you also loose the other healthy circuits in the sub-CU.

In many cases that is not important enough to worry about, but if it is an issue then your alternative is to spilt the tails and feed the 2nd CU from a switch-fuse (typically in the region of 40-63A).

Also you need to consider RCD protection, ideally in the sub-CU as you suggest, but in turn that means you need cable or routing (i.e. not buried/hidden) that permits no "additional" RCD protection. Usual safe bet is SWA. You might still need upstream RCD protection if you can't disconnect on the sub-main PFC (usually TT earth case) but that can be a 100mA/300mA selectivity (short delay) type that gives your final circuit's RCD protection the chance to act first.
 