Can you feed a consumer unit from another consumer unit, It would be supplied by a non RDC protected MCB. Is this allowed as I have always seen switched fuse disconnection units.
 
Depending on the circuit design, then yes…. It’s allowed.

More details please for more explanation.
CU sizes, cable type and size, breaker size, environment….



Welcome to the forum
 
I often do it this way for small extensions / kitchen refurbs etc especially when the exisitng board has a nice spare way.
 
  • Like
Reactions: pc1966
Just to add to the above, it is a perfectly good way of feeding a few circuits elsewhere, such as garage, etc.

However, you get poor fault selectivity on MCB feeding MCB. Basically if your final circuit has a PFC that is able to hit the upstream MCB's "instant" magnetic trip point then both MCBs will fire, and so you also loose the other healthy circuits in the sub-CU.

In many cases that is not important enough to worry about, but if it is an issue then your alternative is to spilt the tails and feed the 2nd CU from a switch-fuse (typically in the region of 40-63A).

Also you need to consider RCD protection, ideally in the sub-CU as you suggest, but in turn that means you need cable or routing (i.e. not buried/hidden) that permits no "additional" RCD protection. Usual safe bet is SWA. You might still need upstream RCD protection if you can't disconnect on the sub-main PFC (usually TT earth case) but that can be a 100mA/300mA selectivity (short delay) type that gives your final circuit's RCD protection the chance to act first.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
southern england
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Can you feed a consumer unit from another consumer unit?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Adam00,
Last reply from
pc1966,
Replies
3
Views
5,983

Advert