Hi, not experienced this before but i have a workshop where the 110v consumer unit (old wylex 3036 board 4way)
Do the board is fed from a 16amp sp mcb from a t0&n board. Then goes into. Standalone transformer wall mounted 3.5kva then into the cu and then to 4x 110v socket outlet.

Ive managed to source a (protek 110v double pole rcd) so i was going to arrange the new consumer unit in this order
2 pole 100amp main switch
30mA 110v 2 pole rcd
4x 16amp mcb
(All protek)

Thankd for any help/guidance
 
110V is really “2 phase” with a centre tapped earth… so only 55V from either phase to earth.

The breakers need to be double pole as there is no earthed neutral on each outgoing circuit for single circuit isolation.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bigspark17

Arms
-
Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
110v consumer unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
bigspark17,
Last reply from
westward10,
Replies
6
Views
221

Advert

Back
Top