so in other words you shoved 500V through the RCD....

Thought RCDs were good for 500V apart from RCBOs on which you have to remember to disconnect any functional earth? If the RCD has been killed, wouldn't that result in a failed test rather than refusal to test?
 
Thought RCDs were good for 500V apart from RCBOs on which you have to remember to disconnect any functional earth? If the RCD has been killed, wouldn't that result in a failed test rather than refusal to test?
may just not test at all....

personally i think theres either a lack of understanding about how to carry out the test competantly from the OP (hardly surprising)

or theres no continuity of CPC someware......

if theres any exposed pipework nearby the OP could prove the no continuity of CPC easily by connecting the earth croc to extranious whilst testing the RCD.....if it lets go then i would dare say its a CPC thing....
 
Try testing live (load side) to earth only(neutral and earth probes)
Did an rcd spur work out cheaper than fitting an rcbo at the board?and where did you site it?Above the ceiling?
 
What film are you watching?

Schindlers Fist?
Womb Raider?
Snow white does seven dwarfs?
School of cock?
Gangbangs of new York?
Here Now go and calm down your getting all heated under the collar lol
 

Attachments

  • 1898171_641289579275061_1813353385_n.jpg
    9.4 KB · Views: 147
I have fitted RCD spurs mid point on light circuits for people when doing work and never had a problem to date, I would think there's something more simple going wrong here such as leafs wrong way over on MFT....
 
may just not test at all....

personally i think theres either a lack of understanding about how to carry out the test competantly from the OP (hardly surprising)

or theres no continuity of CPC someware......

if theres any exposed pipework nearby the OP could prove the no continuity of CPC easily by connecting the earth croc to extranious whilst testing the RCD.....if it lets go then i would dare say its a CPC thing....

Back to your old ways then Glenn.. for a brief moment I thought it looked like you were becoming an adult.

Bit exhausting to keep saying it, so I'll give up after this... but have another read of the thread.
 
New posts

Reply to Cannot get RCD test to work? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top