Yea I would go with that, but OSG doesn't prohibit 'Metal' enclosures as long as the tails are mechanically protected, I guess fed in to the board in conduit or similar.

ATB J
 
Im fairly certain that metal CU's were / are prohibited for domestic TT installs.
Cant remember the reg , might even be from the 16th regs.
Its just something that i remember reading somewhere.
 
I don't disagree with extra protection I was just curious to see if it was an interpretation of the regs or a reg
Eng 54 could you explain to me how you interpret the regs on protecting tails in to an enclosure on a TT ? if the 100mA RCD is in the board, and not external to it how does/can it protect the tails that are from DNO fuse to incomer on RCD ? Not a trick question just a genuine enquiry fella.

ATB J

To be honest with you, for the life of me i cannot understand why you would need an RCD to protect the insulated and sheathed tails entering a metal CU/DB on a TT installation!! If the installation is correctly installed by a competent electrician, that suitably ''Bushes'' the entry of any tails entering a metal CU/DB, ...why would you need protection from an RCD??

I'm not the best person to ask for interpretation of BS7671 regarding TT systems. As to my mind, that whole section needs completely revamping in it's entirety... lol!!
 
I would have thought you could have gunned the RCD out and stuck a main switch in from stock in about thirty seconds, tested the RCBO, and then gunned the RCD back in. If you were that worried.
 
I think it relates to normal leakage currents and high Ze(Ra) resistance. A voltage, albeit small and non existent to dry hands/bodies fully clothed, will be constantly present.

I have measured up to 27V, excessive, between earth and MET before now without the RCD tripping.

When/if a fault develops then you are looking at a potential divider created by a small R1 with a very large Ra but then that's what the RCD is for....
 
New posts

Reply to Can't test RCBO as main RCD trips first - what to do? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
778
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
884
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
625

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock