Looking at a job tomorrow evening for a new 5 bed house +granny flat over a basement floor+ground.

In my initial phone call to the client- down-lights are wanted in the basement concrete ceiling

'which will need to fit cowlings we've already cast into concrete'

I am assuming they are not/don't want too drop the ceiling and have down-lights installed this way.

I have never been involved or even thought about down-light actually recessed into concrete!!

assuming 'cowlings' are maybe hoods that are pre installed before the concrete pour? -how is it wired? pre installed conduits?

any advise or past experience welcome
cheers
 
and surface trunking for the cables ...........................?
well if they

Took a look today so the main contractor has put ‘pots’ in the concrete of the ground floor (basement ceiling) where lights are positioned

And he wants it wired from above

Then concrete screed will then go on top

He wants the wiring laying on the ground floor (for points below) to be protected in copex/mini trunking to prevent damage in the building stage- but doesnt have the budget for a more robust install like galv conduit.

I explained that this would not be rewireable in 50 years time without any demo work!! Which he understands and will be making the client aware (who is actually a tv show architech!!)

Not sure if i want to carry this out or not?

Thoughts...
 
and surface trunking for the cables ...........................?
well if they

Took a look today so the main contractor has put ‘pots’ in the concrete of the ground floor (basement ceiling) where lights are positioned

And he wants it wired from above

Then concrete screed will then go on top

He wants the wiring laying on the ground floor (for points below) to be protected in copex/mini trunking to prevent damage in the building stage- but doesnt have the budget for a more robust install like galv conduit.

I explained that this would not be rewireable in 50 years time without any demo work!! Which he understands and will be making the client aware (who is actually a tv show architech!!)

Not sure if i want to carry this out or not?

Thoughts...
 
so asked the make up of the ground floor (where he wants me to run the cables for the basement level below) ....
  • Concrete Screed – Max temperature 20-30C
  • Reinforcement Mesh
  • Wet Underfloor heating pipes, within the concrete screed, max water temperature 40-60C, not touching your wires/trunking.
  • Electric Wiring within plastic trunking
  • RC Concrete Slab
 
If its the architects house and he has specced it out then he should have done the spec for the electrical work, its not up to you to work it out as you are not the designer, you are the grunt that just does as he is told and gets paid for it.

To me it looks like he is looking at you to find a solution to his design criteria.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

J.C.E

Arms
-
Joined
Location
Earth

Thread Information

Title
casting down-lights into concrete (new build)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
J.C.E,
Last reply from
Squid,
Replies
22
Views
2,505

Advert

Back
Top