The cpc is not insulated, but it is sheathed in T&E. That is considered adequate when part of a cable.
The cpc is allowed to be smaller in fixed installation cables such as T&E because using the adiabatic equation, it is assumed that the duration of the earth fault current is so short that none of the heat energy produced in the protective conductor escapes before the protective device operates. Although not entirely accurate, it is close enough to satisfy BS7671.

Hope that helps :)
Excellent answer and true we hope RCDs will operate at 30 or 40 mA but.....the earth in T&E has always been a smaller dia than the current carrying cables longgggg before RCDs ELCBs were considered a necessity and there is still the question of an un sheathed cale. So what you are saying is if you buy a piece of general purpose three core to wire up a a piece of electrical equipment the earthy core is already sheathed in the outer sheath and there fore a seperate sheath is not necessary. But it is sheathed!:wink_smile:

Surely its not that difficult to put a sheath around it? It would take away the necessity to sheath it at either end when making off. Well as an old stager thats my believe.
Having 'leccy'd' in France a lot of what the French leccy's do is far and away better to the way Brits do it and having a sheathed earth of the same diameter as the current carrying cables is one of 'em.
Sorry being pedantic again I'll get me coat!
Fred
 
Last edited:
Yer right. The drinking up bell used to sound at 10:00 and continue till 10:30 this was in the early 70s (I used to live in Clydebank!!)
Fred

Aye I'm going back to when I was a bairn in the 50's , not to far away from you as it happens . I was talking about Scotland though Trev, rang the bell at half nine and drink off before twenty to ten. Then they used to go back to me grannies with the "carryoot".
 
In Wales,a county could be sunday closed and next door could be open,a pub one side of the river would be 10-30 stop tap,the pub on the other side 11-00

The stampede over the bridge just after 10-30 from the closing pub would have run Bolt a close second
 
rodgearing;589711 So what you are saying is if you buy a piece of general purpose three core to wire up a a piece of electrical equipment the earthy core is already sheathed in the outer sheath and there fore a seperate sheath is not necessary. But it is sheathed!:wink_smile: Surely its not that difficult to put a sheath around it? It would take away the necessity to sheath it at either end when making off. Well as an old stager thats my believe. Having 'leccy'd' in France a lot of what the French leccy's do is far and away better to the way Brits do it and having a sheathed earth of the same diameter as the current carrying cables is one of 'em. Sorry being pedantic again I'll get me coat! Fred[/QUOTE said:
Using twin and earth, when stripping back you must always sleeve the earth with green/yellow sleeving in the back box (or whatever)!
 

Reply to Certificate of competency in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all, Just a quick question, I am an electrical maintenance engineer and have 18th edition, inspection and testing and so on, so I get...
Replies
17
Views
1K
As per Part P of Building Regs, once electrical work is performed by a registered competent person, the installation certificate needs to be given...
Replies
21
Views
3K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
669
A relative recently had an electrical certification done on a rented property. The property was build in 2005 and had previously passed 3...
Replies
25
Views
3K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top