Discuss Checking for breaks On A Long Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Once you test and determine there is a break,the fun can then start, using your meter to measure resistances calculate exactly where along its length that break has occurred
Simply check continuity,on each conductor,until you find O/C....then,pull the copper inner conductor,out of the insulation.
Then,measure the length of that copper,and note it down.
Measure the total length of the cable,deduct the length of the copper,and then measure that distance,from the other end.
....This,is where your break is. ;)
then when he's cut the cable at the break, re-insert the copper conductor he's pulled out, and repair. :D:D:D.
Reply to Checking for breaks On A Long Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB...