Installed a new radial circuit in a garage from an existing CHINT garage unit.

All functioning well (tests fine) until after the RCD test. Then everything, lights etc stops working.

On investigation, while I've got 244V at the incoming side of the main switch I'm getting a reading of between 85 and 166.5 on the outgoing.

Guessing it's knackered the RCDI'll swap it out tomorrow but wondered if anyone else has encountered this fault. I've never touched CHINT gear.
 
Think you missed the point of my comparison..
A 3% failure rate for a life saving device is unacceptable
No not really.
The failure rate of seat belts is offset by the fact that they are tested annually (after the first 3 years), and if they fail the test, they must be fixed or replaced.

Biggest problem with seatbelts is the lap belt type often used for the centre seat in the rear of cars which in the event of an accident can cause severe internal injuries which would not occur with 3 point seatbelts.
Such belts can still be used effectively with many child car seats.
 
Sorry, not interested in seatbelts..
Only the 3% failure rate of a life saving device...
There are statutory requirements in place for earthing.. The use of RCDs in many instances are required to satisfy those statutory requirements..
Do you have any statistics for the failure rates of MCBs?
 
To start with any safety device can fail.
The failure rate according to a report from Electrical Safety First conducted in 2006, was in fact 7.1% falling to 2.8% with regular use of the test switch.

As far as I am aware, there are no statistics for failure of MCBs.
 
A little while back, there was a thread about the reliability of RCDs.
Apparently only 3% of RCDs fail.
Currently there are 3 threads about failed RCDs.

I thought the failure rate was higher than that. I vaguely recall reading so in the Beama RCD handbook. Will have to find it again
 
Think you missed the point of my comparison..
A 3% failure rate for a life saving device is unacceptable

Now you're right, but not completely right.

50% failure rate would be entirely acceptable if you had diagnostics to warn if it had failed. A seat belt for example, might not buckle one day.

Or if these failures failed safe. RCD trips and goes open circuit.

The real numbers you need to look at are the mean time to dangerous failing.

Anyone designing safety circuits or machine design will know all about this.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South East
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
CHINT RCD MAIN SWITCH MALFUNCTION AFTER TEST
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
South Spark,
Last reply from
Bobster,
Replies
19
Views
4,462

Advert

Back
Top