I looked at a job today in commercial kitchen.
They want power run to a 15.5kw cooker, now obviously this would come in around 67a. Applying diversity
it comes to around 27amps.
Would you use a 32amp mcb with 6mm t&e?
Or would you recommend 40amp mcb with 10mm? since it's not a domestic dwelling.
Cable will be run in trunking with conduit drops.