DanBrown

Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...

My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type

My results suggest that a min CSA earth is 1.78mm2 and my cable CPC is only 1.5mm2.

Could someone just do a quick confimation of my answer please...
Is it a problem as such or not?? (still learning testing)
 
Hey.

Havn't got ol red to hand but it sounds about right.

From memory divide 247 by 0.38 to get (I).
(T) comes from APP 3 of ol red. (K) comes from table 43.1 of ol red. (S) obviously is your C.S.A of the conductor you have.

(S) = the square root of ((I) squared x (T)) divide by (K)

Cheers.
 
Last edited by a moderator:
Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...

My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type

My results suggest that a min CSA earth is 1.78mm2 and my cable CPC is only 1.5mm2.

Could someone just do a quick confimation of my answer please...
Is it a problem as such or not?? (still learning testing)


Max impedance for a type c 32 amp is .72
 
Hey.

Got my regs book out now.

So where you have measured voltage as 247V, The equation says to use Uo which would be 230V.

I = 230/0.38 = 605.
K = 115
T = 0.01

So I squared = 366,025
366,026 x 0.01 = 3660
square root of 3660 = 60.50

60.50/115 = 0.52.

S should be greater than 0.52 and you have 1.5 so it's ok.

Hope this helps
 
Thanks for that guys...
Thants a good point for me to remember lenny, use the Uo - 230v and not the actual voltage 247v..

Also in response to the previous question (why use type c breakers) im not sure, we have just had NIC firm in to rewire entire house, and they seemed to fit all RCBO's in type ''C''....
Does anyone have a reason for this?? becuase i cant fink of a answer!!
 
I've installed Wylex Type B RCBOs recently, but I seem to remember TLC didn't have any and I had to go to CEF... I think. Memory a bit cloudy tonight.
 
So RCBO's change to MCB's with age do they?

No? Didn't think so, maybe somebody else was looking for information and stumbled across this.

Please try to be more helpful next time you post.

John.

Hang on a minute, you were replying to the OP by name which is why I replied.

As for being helpful, maybe a quick browse of my 7 and a half thousand odd, other posts may enlighten you!
 
  • Like
Reactions: 1 person
Yeah cmon Lenny, you're getting like Millwall Ken!
 
..Meant to put smiley after that..
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Confirmation of earth size is correct, using adiabatic equation.
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
DanBrown,
Last reply from
jaresquire,
Replies
14
Views
4,534

Advert