Discuss Confirmation of earth size is correct, using adiabatic equation. in the Australia area at ElectriciansForums.net
DanBrown
Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...
My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type
My results suggest that a min CSA earth is 1.78mm2 and my cable CPC is only 1.5mm2.
Could someone just do a quick confimation of my answer please...
Is it a problem as such or not?? (still learning testing)
Hey.
Havn't got ol red to hand but it sounds about right.
From memory divide 247 by 0.38 to get (I).
(T) comes from APP 3 of ol red. (K) comes from table 43.1 of ol red. (S) obviously is your C.S.A of the conductor you have.
(S) = the square root of ((I) squared x (T)) divide by (K)
Cheers.
Max impedance for a type c 32 amp is .72
Hey.
Got my regs book out now.
So where you have measured voltage as 247V, The equation says to use Uo which would be 230V.
I = 230/0.38 = 605.
K = 115
T = 0.01
So I squared = 366,025
366,026 x 0.01 = 3660
square root of 3660 = 60.50
60.50/115 = 0.52.
S should be greater than 0.52 and you have 1.5 so it's ok.
Hope this helps
Thanks for that guys...
Thants a good point for me to remember lenny, use the Uo - 230v and not the actual voltage 247v..
Also in response to the previous question (why use type c breakers) im not sure, we have just had NIC firm in to rewire entire house, and they seemed to fit all RCBO's in type ''C''....
Does anyone have a reason for this?? becuase i cant fink of a answer!!
i know that my local wholesalers only do c type wylex rcbo's... say they cant get hold of b type.
I've installed Wylex Type B RCBOs recently, but I seem to remember TLC didn't have any and I had to go to CEF... I think. Memory a bit cloudy tonight.
So RCBO's change to MCB's with age do they?
No? Didn't think so, maybe somebody else was looking for information and stumbled across this.
Please try to be more helpful next time you post.
John.
Hang on a minute, you were replying to the OP by name which is why I replied.
As for being helpful, maybe a quick browse of my 7 and a half thousand odd, other posts may enlighten you!
Reply to Confirmation of earth size is correct, using adiabatic equation. in the Australia area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
6K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
I'm installing a new supply to a ceremoniously dumped welfare cabin. I can't see any legitimate reason not to apply section 717, welfare units are...