Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...

My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type

My results suggest that a min CSA earth is 1.78mm2 and my cable CPC is only 1.5mm2.

Could someone just do a quick confimation of my answer please...
Is it a problem as such or not?? (still learning testing)
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
T

Tiger

  • Thread Starter Thread Starter
  • #3
You must be logged in to see the message.
 
J

Jono Pashley

  • Thread Starter Thread Starter
  • #6
You must be logged in to see the message.
 
J

John In Afghan

  • Thread Starter Thread Starter
  • #9
You must be logged in to see the message.
 
J

John In Afghan

  • Thread Starter Thread Starter
  • #12
You must be logged in to see the message.
 

jaresquire

-
Arms
You must be logged in to see the message.
 