davesparks
Your right the without tool thing was referring to bath panels not cupboards. I still feel limiting access could make this a C3 instead of 2.
Possibly, but only on one of the various issues that could attract a C2.
Your right the without tool thing was referring to bath panels not cupboards. I still feel limiting access could make this a C3 instead of 2.
It doesn't. But an electric shower mounted in zone 1 is only correctly IP rated for the zone if the cover has not been removed. The cover of an electric shower can only be removed by use of a tool. Same principal could be applied to any item of electrical equipment, if one was desperate to make it comply.That would help, however where in the regs dose it define a tool or a key as being a way of avoiding zones?
Who is the they that wants the eicr done?What’s your thoughts of a new renovated house that has the consumer unit in the bathroom. It’s situated above the bath in a cupboard. It was brought 2 weeks ago and have no certs. They want a Eicr done. Obviously the sockets has to go too.
Thanks
I’m away and don’t have the book with me however from memory I think 701 discusses walls and partitions, not cupboards. What this mostly boils down to is suitability for the environment, which is a clear fail. However I’m also caused to question if it’s going to satisfy the requirements for all wiring to be RCD protected - I’d have thought the incomer is highly unlikely??
See #38. Is said cupboard providing an EFFECTIVE barrier.An outlet socket on a landing directly outside a bathroom door less than an MTR away would be compliant as it's behind a door.
An airing cupboard with electrical heating etc in a bathroom behind a door is compliant.
Electrical equipment under a bath is also compliant.
An electric shower which has just a plastic cover and also has uninsulated connections inside is also compliant.
Because is behind a barrier, it's technically not in a zone.
If not in a zone, then IP rating etc shouldn't be an issue. ?
Posted while I was writingSee #38. Is said cupboard providing an EFFECTIVE barrier.
701.32.1 ........................doors, floors and fixed partitions may be taken into account where these EFECTIVELY limit the extent of locations containing a bath or shower as well as their zones.
And see #10 ;-)See #38. Is said cupboard providing an EFFECTIVE barrier.
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
THis...Rules and regs dont make a lot of sense at times . For me this install is a Joke and a mockery of what is safe etc . That telephone shower hose can easily reach and spray water directly onto the cupboard .lets see if anyone happy with the regs would let their child take a shower in this bathroom !It doesn't. But an electric shower mounted in zone 1 is only correctly IP rated for the zone if the cover has not been removed. The cover of an electric shower can only be removed by use of a tool. Same principal could be applied to any item of electrical equipment, if one was desperate to make it comply.
I'm just playing devil's advocate here, there's no way I would want a consumer unit anywhere in a bathroom.
I think most would agree that the situation is far from ideal and I doubt many, if any would commission such an installation.
Maybe something like this would be acceptable?
![]()