That would help, however where in the regs dose it define a tool or a key as being a way of avoiding zones?
It doesn't. But an electric shower mounted in zone 1 is only correctly IP rated for the zone if the cover has not been removed. The cover of an electric shower can only be removed by use of a tool. Same principal could be applied to any item of electrical equipment, if one was desperate to make it comply.

I'm just playing devil's advocate here, there's no way I would want a consumer unit anywhere in a bathroom.
 
What’s your thoughts of a new renovated house that has the consumer unit in the bathroom. It’s situated above the bath in a cupboard. It was brought 2 weeks ago and have no certs. They want a Eicr done. Obviously the sockets has to go too.

Thanks
Who is the they that wants the eicr done?
 
Rather than trying to code against 7671, why not just go for that jugular; EAWR Regulation 5 and 6 (Strength & Capability and Adverse or Hazardous Environments) as these apply while you are AT WORK undertaking the EICR. If we must put a reg against it then I offer up 132.5.1; Electrical Installation must be suitable for the environment for which it is located and expected to operate in
 
I’m away and don’t have the book with me however from memory I think 701 discusses walls and partitions, not cupboards. What this mostly boils down to is suitability for the environment, which is a clear fail. However I’m also caused to question if it’s going to satisfy the requirements for all wiring to be RCD protected - I’d have thought the incomer is highly unlikely??
 
Non sparky comment :
Irrespective of regs, I would have expected a survey to have alerted me to the issue and consequently would have purchased only if I could afford to get it moved.
I would immediately secure the doors and put a warning notice on them. Despite this I would worry about condensation.
Would an IP?? Enclosure prevent high levels of humidity around the electronics of rods/rcbos etc.? Or do they run warm enough even at zero load that I should not be concerned?
Personally, my sparky would have to work hard to convince me NOT to move it. An elcr would presumably help sparky to determine how problematic a move is likely to be .
 
I’m away and don’t have the book with me however from memory I think 701 discusses walls and partitions, not cupboards. What this mostly boils down to is suitability for the environment, which is a clear fail. However I’m also caused to question if it’s going to satisfy the requirements for all wiring to be RCD protected - I’d have thought the incomer is highly unlikely??

An outlet socket on a landing directly outside a bathroom door less than an MTR away would be compliant as it's behind a door.

An airing cupboard with electrical heating etc in a bathroom behind a door is compliant.

Electrical equipment under a bath is also compliant.

An electric shower which has just a plastic cover and also has uninsulated connections inside is also compliant.

Because is behind a barrier, it's technically not in a zone.

If not in a zone, then IP rating etc shouldn't be an issue. ?
 
An outlet socket on a landing directly outside a bathroom door less than an MTR away would be compliant as it's behind a door.

An airing cupboard with electrical heating etc in a bathroom behind a door is compliant.

Electrical equipment under a bath is also compliant.

An electric shower which has just a plastic cover and also has uninsulated connections inside is also compliant.

Because is behind a barrier, it's technically not in a zone.

If not in a zone, then IP rating etc shouldn't be an issue. ?
See #38. Is said cupboard providing an  EFFECTIVE barrier.
 
701.32.1 ........................doors, floors and fixed partitions may be taken into account where these  EFECTIVELY limit the extent of locations containing a bath or shower as well as their zones.
See #38. Is said cupboard providing an  EFFECTIVE barrier.
And see #10 ;-)
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
 
It doesn't. But an electric shower mounted in zone 1 is only correctly IP rated for the zone if the cover has not been removed. The cover of an electric shower can only be removed by use of a tool. Same principal could be applied to any item of electrical equipment, if one was desperate to make it comply.

I'm just playing devil's advocate here, there's no way I would want a consumer unit anywhere in a bathroom.
THis...Rules and regs dont make a lot of sense at times . For me this install is a Joke and a mockery of what is safe etc . That telephone shower hose can easily reach and spray water directly onto the cupboard .lets see if anyone happy with the regs would let their child take a shower in this bathroom !
 
I think most would agree that the situation is far from ideal and I doubt many, if any would commission such an installation.

The problem isn't whether or not anyone likes the situation presented, but what problem it actually presents from a regulatory perspective.

Personally, I'd insist on the removal of that double socket as a precondition of working on the installation, but could only recommend its removal if carrying out an eicr.

Edit: meant to quote the previous post from @LukeD and not even going you attempt editing on a mobile.
 
Maybe something like this would be acceptable?

It would improve the situation but there would still be inadequate access to the CU.
Having to stand in a bath is not an adequate access arrangement.
 