Hi, i've got a few questions regarding consumer unit connections;

My first question: On a split load consumer unit does every circuit need to be protected by RCD e.g. lights ?

Second question: If a high integrity consumer unit has two unprotected circuits next to the main switch, do they have to have RCBO or would MCB protection be sufficient enough to meet the 17th edition wiring regulations?

Third question: A 6mm SWA cable going to a shed to a small consumer unit with RCD - supplying a ring main and lights - will the cable need 32amp RCBO on the main consumer unit in the house or just 32amp MCB protection?

Thanks in advance.
 
Hi, i've got a few questions regarding consumer unit connections;

My first question: On a split load consumer unit does every circuit need to be protected by RCD e.g. lights ?

No, but the will need to be surface mounted cables or buried deeper than 50mm with earthed meatalic capping.

Second question: If a high integrity consumer unit has two unprotected circuits next to the main switch, do they have to have RCBO or would MCB protection be sufficient enough to meet the 17th edition wiring regulations?

As above

Third question: A 6mm SWA cable going to a shed to a small consumer unit with RCD - supplying a ring main and lights - will the cable need 32amp RCBO on the main consumer unit in the house or just 32amp MCB protection?

IMO It would be best to RCBO as all final circuits will then be protected as well as the distribution cable.

Thanks in advance.


see bold
 
circuits in bathrooms will need rcd protection unless bonded to current regs also anything with a socket on it will require rcd as previously stated surface and mechanically protected does not but it is doubtfull that cables burried in walls will be 50mm deep after all coz 5cm is deeper than any plaster theese days.
you would be better off getting a dual rcd board then your covered as rcbos are a bit pricey
the armoured going to the garage would be ok without rcd if you had the sheathing terminated as this counts as mechanical protetion,with an rcd in the garage although i would be inlined to protet ths aswell , some clown will point out you have an rcd supplying an rcd,(in series) but thats not going to bother anything unless a bigger one is fitted in the garage than the house
 
You shouldn't have 2 x 30ma RCD's inline,

MCB on the SWA at supply (Non RCD), Then RCD as incomer on shed CU.

This would go on the unprotected way on a high integrity CU in main house as an example.
 
------------------------------------------------------------------------------------------------------------------------------------------------

MCCANT

I must be that clown!! lol
 
Last edited by a moderator:
circuits in bathrooms will need rcd protection unless bonded to current regs

Not correct...To comply with 17th edition all final circuits in a bath/shower room must be RCD protected regardless of whether supplementary bonding is in place or not............supplementary bonding may be omitted providing ....
1. All final circuits are 30ma RCD protected.
2.Required disconnection times are met.
3.A continuity reading of <1667ohms is measured between conductive and extraneous conductive parts within the bath/shower room.
 
Hi al

question !!!!

DB1 in house ( dual rcd ) feeding small ccu in garage with swa !!! this in turn will feed a swa to a garden shed!!!

Question !!!

i fully under stand 30ma rcd,s in line is a no no !!! so can i install the garage unit with just a main swith and no rcd/main switch and in turn feed the shed via swa from ccu in garage !!!

Question !!!

because of feed from db1 being on a rcd i can not tt the garage ccu so will have to export the earth from db1 . iunderstand you can do this as long as there is no extranios conductive parts in out buildings also i am going to rely on the rcd in db1 ( house ) to protect all the out side installation!!!! i know that if a neutral earth fault occures it will knock half the board out in db1 but can not see any other way round it !!!

Question !!!!

would you guys and girls approach it in the same manner

thanks
Richard
 
yes your right ,although if doing periodic inspection you found no rcd in bathroom but it was bonded you could get away with a code 4 for it
not that it helps any in this case
 
i do it all the time , will argue all day about something then pull out the regs and find i m wrong, normally insult a few people along the way aswell
 
i need advise from the 17th as ive been made redundent as surley many of you can relate to ,i just want to no some thing,can any body help ?
 
i would put some tale blocks on and fit a seperate 1 way unit in the house for the garage
Make sue you use an RCD unit with 32 Afor sockets if 1 socket a 16 A MCBO and 6 A for your lights,And always get it certified.So no a 1 way unit ant gud,you got to remember cable size,contaiment and above all saftey.
 
its 5amish iv just got in fea a night shifty n found this thread a lot more enjoyable than the Snippity Snip one i read yesterday moirning Im now off to ask the wife if 5cm=50mm n see her reaction ( she can be a bit blunt as to just how stoopid some ppl r )
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Consumer Unit Questions
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
33
Unsolved
--

Advert

Thread statistics

Created
ta-electrical,
Last reply from
mogga,
Replies
33
Views
17,509

Advert

Back
Top