Appreciate a bit of advice regarding this that I'm doing in the morning-

Consumer unit upgrade in house with 6mm gas & water bonding existing (leaving bonding as it is). Existing rod in house with 6mm up to CU.

(Existing install) From a TT system in the house there is a 2.5/1.0 T&E running to a detached outhouse (perhaps, four meters from the back of the house) feeding an existing fuseboard in there with BS3036 fuses for 15A sockets radial and 5A one light.

The outhouse has a copper water pipe supplying a washing machine. This isn't bonded where it rises from the concrete floor in the outbuilding and there isn't a seperate rod in there. The only earthing of anything in there is the 1.0mm CPC of the T&E submain & CPCs of light/sockets.

Am I right in thinking that the CPC in the T&E won't suffice in the requirements for equipotential bonding in the outbuilding (it appears that the T&E is ran under the concrete back yard in plastic conduit.. many years ago). If I install a rod & earth conductor to the existing BS3036 unit in the outbuilding and bonding between this unit & the copper pipework in the outbuilding, should I insulate the 1.0mm CPC in the T&E submain from the outbuilding installation (at the outbuilding end)? Or leave it connected at both ends- in the house and the outbuilding. If either is acceptable would it be best practice to leave it connected both ends?

I am quite aware of requirements when exporting TNS and TNCS but I've never came across TT in the main building with an outbuilding where bonding is required.

This is hopefully obvious to one of you who may read this before tomorrow :)
 
Something is certainly obvious, but i'll limit my comments to the job you are asking about.

I would not be happy with a T&E underground in a pvc pipe for a start. you are right that 1.0mm is too small for a binding conductor. Ideally you would get a 6mm to the outbuilding and add a rod there connected back to the MET to help the Ra of the installation. seperating the outbuilding and adding earth electrodes there will require the installation of RCD protection to the outbuilding.
 
Thanks dave. It's for an agent and unless absolutely necessary they wouldn't have it done. We are moving some sockets around as there is a new kitchen going in, and the existing consumer unit is damaged so needs replacing.

The existing T&E submain will be 30mA RCD protected in the house. It is in plastic conduit but below the concrete, the IR test on it is fine (>299 @ 500V) & you can see where it comes out of both ends indoors. Despite outbuilding being very close to the house, it wouldn't be easy to get back to the CU in the house from the outbuilding (opposite end, laminate everywhere etc).

A 6mm can't be ran to the outbuilding unfortunately.

If I install a rod to the outbuilding, what should I do with the 1.0mm CPC in the submain at the outbuilding end? I can't see any reason to disconnect it as both sides are TT, but I'm not sure.
 
Something is certainly obvious, but i'll limit my comments to the job you are asking about.
I don't mind if you elaborate!

Your OP reads as though you haven't got a clue how to install a TT system properly. It sounds like you are planning to have just a single rod for the main earth and that you don't understand either the regulations concerning earthing of multiple buildings nor the theory behind them.
 
I am not installing any new in the house, there is an existing rod in the house is at the opposite end of the building, below the CU, I would hazard a guess that its 30-40m in a straight line from there to where the outbuilding is.

I would guess that (terraced housing) the rod in the house next door is perhaps 2m away from the rod in the house we are working in, are there any definitions / good practice measurements of being far away enough?

I don't see any reason to need more than 1 rod at the outbuilding to acheive <100 ohms

If the outbuilding wasn't in use I would have left it disconnected, but they will want it connecting to the new CU in the house due to the washer being out there, but I want to make sure the arrangements in it are acceptable first!
 
What is the Ra of this one existing rod? How long is it and what diameter is it? Is it really inside the building?

What has 100 ohms got to do with anything? The point of having multiple rods is to achieve stability through depth, a low Ra and the ability to safely handle the maximum current which may flow under fault conditions.

In a scenario where an earth fault occurs in the house, what do you think would happen to the cpc in that submain if you connected it to the electrode at each end?
 
just a single rod for the main earth = measurement at this existing rod was about 35 ohms, why would I need more?

and that you don't understand either the regulations concerning earthing of multiple buildings nor the theory behind them
= this is an existing install with outbuilding 4m away with two sockets and a light. I'm aware that the existing arrangement isn't satisfactory but thats why I'm asking on here.

:49: I'm well aware that some on these forums will bang in multiple rods until their reading is as good as TNS! However if the reading is acceptable, it's acceptable. Especially for a letting agent
 
How did you measure the 'about 35ohms' ? A 3 wire fop test? Or was it a loop test with the rod disconnected from the installation?

What do you define as being an acceptable reading? Bearing in mind there is no definition in the regs, it's up to a professional to make their own assessment.
What do you mean by 'especially for a letting agent'? Are their lives worth less than other peoples and so it's ok to install substandard earthing ?
 
I don't know for sure, but I would say 5/8" and probably 4 ft if it isn't extended.
Yes it's inside (under the hallway floor as you come in the front door), as will be every other electrode in the 2000 identical houses in that area!

I've always used 100 ohms as a guide for acceptable / likely to be stable as it's what I was taught during my apprenticeship, 2391 course, the way it was done at NIC companies ive worked for & it seems it's acceptable with NAPIT who I'm with.

I don't think anything would happen to that submain as RCDs would operate.
 
My best advice is to check with the local DNO to see if a PME connection is available, but he'll still be at a loss as to what to do about the outbuildings extraneous pipework... He'll probably just bung a twig in and call it a day.... Hasn't even bothered giving us the existing Ra value for the the main house.....

EDIT....Ah i see he's just given the house Ra value...
 
Last edited by a moderator:
Loop test with rod disconnected when I made a brief visit the other day.

"What do you mean by 'especially for a letting agent'? Are their lives worth less than other peoples and so it's ok to install substandard earthing ?"

What I mean is, if something doesn't need doing, it won't be paid for. If I can install a rod and bonding to the outbuilding, and that is acceptable, then that will get done. If that isn't acceptable, and a new submain is needed e.g. 6mm3C SWA, lifting of laminate floors from front to back etc, and they ask someone else for a quote who goes and puts a rod & bonding in the outbuilding AND THAT IS ACCEPTABLE, I may lose out on future work from the agent.
 
Because I want to know what the "bare minimum" is that will comply for me to be able to upgrade the consumer unit in the house and reconnect the submain. I don't want to tell them that the tenant needs to take a day off work & move all their furniture & all the flooring needs to come up etc. to put a new submain in from the front door to the outbuilding over the back yard IF IT ISN'T NECESSARY!

"What is the point in asking questions" whats the point in the tone of these replies-
"Something is certainly obvious, but i'll limit my comments to the job you are asking about"
"What do you mean by 'especially for a letting agent'? Are their lives worth less than other peoples and so it's ok to install substandard earthing ?"
"To be honest i just can't be arsed"
"He'll probably just bung a twig in and call it a day"
I think you're trying to help but equally you want to shoot me down at the same time haha

Please tell me what would be wrong with the following-
Keep existing 2.5mm submain from 20A 30mA RCBO in house.
Disconnect 1.0mm CPC of 2.5 t&e in outhouse.
Install rod & bonding in outhouse.

Be as condescending as you like if you answer the question
 
Your OP reads as though you haven't got a clue how to install a TT system properly. It sounds like you are planning to have just a single rod for the main earth and that you don't understand either the regulations concerning earthing of multiple buildings nor the theory behind them.
Go on then,what are the regulations then? Where is there a requirement for more than one earth electrode for a multiple building install from the same source of supply?
 
Go on then,what are the regulations then? Where is there a requirement for more than one earth electrode for a multiple building install from the same source of supply?

The regulations require that any Protective conductor common to multiple buildings or earthing systems be sized adequately to handle the highest possible fault current from either installation. GN8 is the best source of info on this with clear diagrams and explanations.

There is no regulatory requirement for multiple electrodes in that situation, bit I never said there was.
I have said multiple rods will be required to make up an acceptable electrode, but this was based on the assumption that standard 4' rods will be used, obviously if he uses 10' rods then it's a different story
 
The regulations require that any Protective conductor common to multiple buildings or earthing systems be sized adequately to handle the highest possible fault current from either installation. GN8 is the best source of info on this with clear diagrams and explanations.

There is no regulatory requirement for multiple electrodes in that situation, bit I never said there was.
I have said multiple rods will be required to make up an acceptable electrode, but this was based on the assumption that standard 4' rods will be used, obviously if he uses 10' rods then it's a different story

"It sounds like you are planning to have just a single rod for the main earth and that you don't understand either the regulations concerning earthing of multiple buildings nor the theory behind them."

Well I'd suggest the above statement is somewhat misleading concerning regulations.
Personal preference on earthing is another matter, but on so many threads on TT installs personal preference seems to be confused with actual requirements.
 
"It sounds like you are planning to have just a single rod for the main earth and that you don't understand either the regulations concerning earthing of multiple buildings nor the theory behind them."

Well I'd suggest the above statement is somewhat misleading concerning regulations.
Personal preference on earthing is another matter, but on so many threads on TT installs personal preference seems to be confused with actual requirements.

The above statement was a reply to his request that I share the opinion that I previously had said I would keep to myself.

I cannot see how the statement could be misleading to anyone with a working knowledge of the English language.
 
What are the actual requirements?

You'll find them in Bs 7671.
If it's not in there it's not a requirement.
A prime example is the NICEIC 'max Ra of 100 ohms'.

BS 7671 is not teh be all and end all, there is a seperate british standard (BS7430 'Code of practice for protective earthing of electrical installations') specifically for earthing which is referenced in bs7671.

BS7671 requirements are pretty straight forward, it needs to be designed to withstand damage, allow for increase of resistance due to corrosion, be of a type and depth that soil drying and freezing will not increase the resistance above that required.
A 4' rod is not going to be deep enough to avoid drying out or freezing from affecting it.
 
A single rod is not necessarily only 4ft long.
The only point I want to make here is that regardless of whether you approve or not the lacklustre requirements of bs 7671 with regards to TT systems are nevertheless the only requirements an electrician carrying out a small TT system need comply with.
By all means slate those requirements as wholly inadequate but please dont forward your own views on it as 'requirements'.
 
Please tell me what would be wrong with the following-
Keep existing 2.5mm submain from 20A 30mA RCBO in house.
Disconnect 1.0mm CPC of 2.5 t&e in outhouse.
Install rod & bonding in outhouse.

Be as condescending as you like if you answer the question

If that water pipe you bond in the outhouse is actually extraneous then it will more than likely provide a much lower resistance earth path than the rod you install, potentially making that rod redundant and pointless. Now if you took the time to read your regulations book you would know whether it is acceptable to use the water pipe as an earth electrode or not, and if it is acceptable to use the water pipe as a bonding conductor.

Regulations 542.2.6 and 543.2.1 are concerned with this, GN8 gives further help on understanding them. If the water pipe is privately owned, you can take precautions against it being disconnected and it has suitable CSA then the absolute bare minimum allowed by the regulations may not require you to add any rods.
 
Just to throw a spanner in the works;
A possible scenario could be that a Water/Gas supply combination could be of a much lower resistance than can be achieved by earth rod in some area's. With BS7671 not permitting the use of such a means as an earth path (unless privately owned) then where does an electrician stand having to connect all to the MET, as effectively such an installation will be heavily reliant on the extraneous pipes?
Considering some premises may not have the opportunity for additional rodding or plates etc.
 
Just to throw a spanner in the works;
A possible scenario could be that a Water/Gas supply combination could be of a much lower resistance than can be achieved by earth rod in some area's. With BS7671 not permitting the use of such a means as an earth path (unless privately owned) then where does an electrician stand having to connect all to the MET, as effectively such an installation will be heavily reliant on the extraneous pipes?
Considering some premises may not have the opportunity for additional rodding or plates etc.

look at the post above yours.
 
I don't know where he is, it could easily be the frozen north. They have icebergs and polar bears everywhere north of Watford don't they?

...The day before yesterday,i was running back and forth,outdoors,taking readings with an AC/DC clamp ammeter,alternating between loads,(see what i did,there...)...and get thrashed with the hail storm...

...Me tee-shirt was soaked :joker:
 
Afternoon everyone, just to update the thread with regards to the job to help anyone who reads this in the future in a similar situation. I installed a 4ft rod to the outbuilding, 80 Ohms. Bonded the water. Phoned NAPIT technical support who advised me that it was acceptable to leave the CPC in the submain T&E connected, however if I wished I could disconnect it. I left it connected.

I left the existing rod in the house as I found it, tested & reconnected it to the earth bar in the new CU.

Now lets not have any bickering, enjoy the bank holiday weekend!
 
My preference would be <1Ω

So where does 80Ω come from?
Would it be that it just happens to be 80Ω on this installation and you can grab the money and run without any real work?
 
My preference is also for <1 ohm. I've done it dozens of times, my record is still the same. I've not beaten 0.29 yet. Did one last week and got 0.58 which I was pretty happy with.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Consumer unit upgrade TT system
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
63
Unsolved
--

Advert

Thread statistics

Created
monkeyhanger,
Last reply from
baldsparkies,
Replies
63
Views
9,446

Advert

Back
Top