agree with glen, I would just add a 2.5 to the connection plate and connect to a spur as well, or a single socket if the oven is under 3kw
the `3KW` you refer to is for cookers fed from a ring final.....
its 2KW by the way

APP 15 fig 15A (iii)....
 
can't come off the ring as the sockets are high level behind a splashback. all the sockets low level are for the appliances and fed from fcu's in the cupboard
 
yeah i am going to use the connection unit to spur off. just explaining to sykraps why i can't come of the ring
 
yeah i am going to use the connection unit to spur off. just explaining to sykraps why i can't come of the ring
good lad....
simple to do....compliant..
of you go to it in the mornin....

- - - Updated - - -

dont forget to test the circuit first will you....get an R1 R2, IR and a Zs...good....
 
just explaining to sykraps why i can't come of the ring

I was not suggesting that you come from the final ring circuit as I said I would use 6mm from the cooker circuit to supply a feed via a SFCU, my comment was relating to glennsparks response to my post.

I was wondering why he states that we can spur from a 40a circuit using 1.5 or 2.5 t+e but we can't spur from a 32a ring in less than 2.5 t+e unless the cable is fused down first.

I don't have bs7671 to hand but I am certain that that is the way it is drawn in the apps
 