The oven I can believe, mine is 2.8kW so would be OK on a 16A RCBO. But a typical 4 ring induction hob is around 7.5kW so a 13A plug seems highly optimistic and needs careful checking.induction hob and oven have arrived onsite and both suggest a 13amp supply is suffice.