Discuss Crabtree starbreaker rcd fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Thanks sparkswillfly, if this were the case would the rcd not test normally? Instead we've had two rcd's that will not trip at x1 or x5 and one even tripped with all mcb's on the off position, no loads and no test equipment.?
Do a ramp test with all normal loads running then do a full rcd test with all loads disconnected this will give you the difference which is the leakage present under normal conditions been a tt system clamping the earth on the rod might not give you all the leakage as it may choose other routes as well, also to be noted is neighbouring premises with leakage can in some situations create nuisance tripping too when this starts been the case or similar unresolved reasons then the expensive option of main switch and full board or rcbos instead this gives easier diagnostics if fault is present, and consider several visits will start to cost alot it can sometimes be just as easy to do this for similar cost.
Reply to Crabtree starbreaker rcd fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Hi, I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can...
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...