Hi guys,
Got job ...studio flat just done some odds and ends that requires i put new RCD CU in property.
Very small load currently being fed by T&E from OLD wylex MCB in cupboard on ground floor. Question is The cable of which i did not install
is run (from what i can see) under floor boards into riser under more floor boards, to the CU in studio (CU in studio is about 6" from floor in cupboard.
Opinions on whether a RCD S type should be in place to protect sub main cable. only part of T&E exposed is under the stairs which is an electrical cupboard. rest under floor etc.....
you only need RCD protection on your feed if that feed is buried <50mm in a wall without earthed protection. if it was you'd have to fit a 30mA RCD anyway.
What though if this cable is running <50mm from underneath of floor boards as many a hole has been drilled or cut....
obviously not buried but nails through floors etc etc......would that be situation whether discernment might be required. I mean i have no idea of finding that out but as im dealing with that circuit would i be responsible? Or as its just New CU in studio flat am i not responsible for the condition and arrangements of supply feed? thought i would be
BS7671 specifically says cables buried in walls. (522.6.101). no mention of floors.
Reply to Delay time S type RCD or not RCD in the UK Electrical Forum area at ElectriciansForums.net
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Hi all, Just done an EICR and all tested fine, until I got to the RCD's. It's a dual RCD board, not sure if it's TNCS or TNS as it's a top floor...