Hi All, opinions please, just been to a property that has a 6mm cable ontop of 200mm of loft insulation so not buried. What de-rating factor would everyone apply to this
Would it help if i could get it in some big trunking?
 
I would not be de rating cable being on top of insulation, but it should be adequately secured along its length.
If this is a loft, you might need to de rate for ambient temperature.
 
I would not be de rating cable being on top of insulation, but it should be adequately secured along its length.
If this is a loft, you might need to de rate for ambient temperature.
I imagine it must pass through the insulation at some point so 0.68 off the top of my head.

These

Clipped direct, with adjustment for ambient, or through insulation (depends on thickness @ that point(s) ) or whatever the rest of the run is whichever is the largest de rating
 
Laid on top then I personally would not apply any correction factor

laid underneath for most of the run then its about 0.6 or something
 
Laid underneath would depend on the amount of insulation ie T&E above a plasterboard ceiling covered by thermal insulation not exceeding 100mm would be reference method 100, exceeding 100 mm would be 101, from there you would look at the appropriate table in appendix 4 for the ccc of the cable.
You may need to apply further correction factors where applicable.
 
Last edited:
Laid underneath would depend on the amount of insulation ie T&E above a plasterboard ceiling covered by thermal insulation not exceeding 100mm would be reference method 100, exceeding 100 mm would be 101, from there you would look at the appropriate table in appendix 4 for the ccc of the cable.
You may need to apply further correction factors where applicable.
Thanks all for your thoughts.
As i said cable is on top of insulation and not underneath.
Very hard to clip to anything as there is no slack to move cable so basically just sits on top.
Wonder if there is any merit in placing in some big trunking, 50mm x 50mm, but again what reference method would this be classed as?
 
Thanks all for your thoughts.
As i said cable is on top of insulation and not underneath.
Very hard to clip to anything as there is no slack to move cable so basically just sits on top.
Wonder if there is any merit in placing in some big trunking, 50mm x 50mm, but again what reference method would this be classed as?
Just leave it clipped above, installing it in trunking would be reference method B and will reduce the ccc , further to any other factors.
 
The question is does it penetrate the insulation and thus become totally enclosed by insulation. If less than 0.5m then derating will have to be applied. Unless it goes past the insulation and down to (say) the shower.
 
Sounds to me like it’s a problem for the donut who decides they needs another 100mm of insulation on top....be unusual if it doesn’t pass through the existing insulation at least somewhere though......
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dronfield
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Derating cables laid on top of loft insulation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
briefcasedan,
Last reply from
Baddegg,
Replies
12
Views
6,569

Advert

Back
Top